Lost Art Of Heating Revisited Question

Hello All,
In "The Lost Art of Steam Heating Revisited" on Page 81. There is a suggestion:

"If you have to submerge a tankless coil in the summertime, do it by hand."

I'm confused. How do I submerge a tankless coil by hand. In my "fixed mindset" I picture only one location for a tankless coil. I might have this mixed with an indirect.

Thanks for any help.

Comments

  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    edited October 2019
    I believe it means to manually fill the boiler until the coil is fully submerged in the water. Rather than setting the LWCO / feeder high enough to cover it all the time, leading to a water level that is too high in the boiler for producing quality steam.
    Never stop learning.
  • Pipestretcher
    Pipestretcher Member Posts: 6
    So that makes sense.

    Earlier in this section there was mention of raising the LWCO, which raised the water line and that caused occupant displeasure: No heat (due to reduced header to water line distance), and water hammer.

    So does that mean that raising the water line in the summer to cover the coil will cause water hammer? (No heat will be a desire). Or is the water line height change minimal. It seemed as though the height was needed in the example herein? (All this is very helpful by the way - for reader)

    Thanks
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    I don’t deal with residential work too often, I do mainly commercial. I’ve had to do this with commercial boilers in the past. They would have a second control on them called an aquastat, which senses temperature rather than pressure, and a switch that adds the aquastat into the control circuit. They would manually fill the boiler until the coil was submerged, and the Aquastat would cycle the boiler on temperature rather than steam pressure (so it would never be making steam).

    I’m not sure what other way there would be to do it unless you have a valve in the outlet piping from the boiler. If so you could isolate the boiler and let it run on steam pressure. If you can’t isolate the boiler then I’d imagine it would indeed lead to hammering and send out heat in the summer which wouldn’t be good. I don’t have experience with residential though so I’m not sure how it’s typically done.
    Never stop learning.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,513
    Yes, what Mike said. Thanks.
    Retired and loving it.