vitodens 200 additional circulator
gobucks823
Member Posts: 24
I'm adding an additional zone (will be zone 2) to my Vitodens. Does the second zone circulator get wired to output 157? I'm not finding in the manual and I could've sworn there are connections for 2 zone circulators on the boiler. Am I wrong?
The Vitodens 200 has only one zone dedicated to space heating. The boiler is designed to work without a thermostat and maintain room temp through constant circulation.
You need to add a 2 zone switching relay. I've seen it done but dont know exactly how. The application I saw had 2 hydro air zones, 3 radiant zones, and an indirect. I dont think it's as simple as connecting the relays dry contacts to taps 1-2 on the 143 external block. Maybe others here more experienced with Viessmann can help. Coding addresses will also need to be reprogrammed I believe.0 -
Ok. That is making some sense then for why every piping description in the manual with more than 1 zone shows the second zone with a mixing valve.0
I'll pick up a 3 zone pump switch on Monday. I was planning on not using thermostats and allowing the constant circulation of the zone pumps. Do I just jumper the stat connections on the switch together? I assume I remove my existing single zone pump from 28/20 on the boiler and wire to the switch? Do I wire 120v to it externally or is there an output on the Vitodens for this... or does the 28/20 go to the 120v connection on the zone switch?0
What model 200? They have what’s called an “external demand” too that can be set up0
B2HA 280
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 163 Indoor-Air Quality
- 71 Pipe Deterioration
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
