Radiant Heat Expansion- Pumps, Zone Valves, Zone Controller
BenG
Member Posts: 10
I have a 200K BTU Noritz hot water boiler (max 140F) that supplies DHW directly, and through a heat exchanger heats water for a 1500 sq. ft first floor only radiant heat system. There is a circulator pump just outside the boiler that moves the DHW and a 2nd pump for the radiant water loop. Controlling this is a two zone i-Link controller with the radiant heat system on Zone 1 (Zone 2 is empty). Physically next to the Zone 1 pump is the start where a Zone 2 pump could be added. For reference, I did not install this system it came with the house.
I am looking to add heat to 2 unheated rooms (each less than 200 sq. ft) . To do this I am considering adding a Tomotoyi HC-20 to each room, but I am stuck how I should do the pumping, zoning, and plumbing.
- Should the heat convectors be in series with each other? If so should I use mono-flow tees or zone valves to isolate? I want to maximize the available hot water to each system, so I am leaning towards mono-flow tees and zone valves so that if both demand heat the 2nd unit will get hotter water than it would without the tee. Thoughts?
- The heat convectors have their own thermostats. If I use zone valves, and connect the HCs to the valves, can I wire both valves to the future 2nd zone pump? My thought process is... If one HC demands heat then pump turns on. If one HC was running and then the other HC wanted heat the 2nd valve would open but since the pump is already running nothing bad happens?
- With my current controller, can I have two zone valves wired to a single pump? Or, do I need a three zone controller, but 2 pumps (and I would jump Pump 2 and 3 together?).
thanks!
thanks!
diagram of my existing set up and Pump 3 plan
I think you could simplify things a bit here. Instead of the three way zone valves, I would use two way zone valves. No need to mix the temperature down for convectors. With the 140 hot water setting that heat exchanger wont put out more than 130 degrees. Then you could eliminate the check valves and mono flow tees.I am the walking Deadman
Hydronics Designer
Hydronics is the most comfortable and energy efficient HVAC system.1 -
Yes I agree. After further research I am planning on using a zone valve manifold from Cross and piping each HC directly to and from the manifold. This system connects to a single circ pump so I think that should be all set now.
Question on the piping...
- Both circ pumps are connected through a common return to the heat exchanger...is that okay? Pump 2 does not have a built in check valve. Should I add one?
- Do I need check valves to separate the return flows as I diagrammed?0 -
The pump leading to the HC's does not need a check valve because the zone valves will shut off the flow when the zones are off. The radiant zone needs a flow check. A check valve isn't good enough. A check valve just stops the flow from going backwards. A flow check stops both forward and backwards flow. When the radiant pump comes on it produces enough force to push through the flow check. Flow checks are very common and a standard in our industry.I am the walking Deadman
Hydronics Designer
Hydronics is the most comfortable and energy efficient HVAC system.0 -
My zone 1 radiant pump is a grundfos up26-99 without a check valve built in. I purchased a replacement valve for the UP26 series and was planning to install it on this pump. Is what you mean or do you mean a standalone valve?0
@BenG
The check valves that come built into the pumps are all flow checks. If the pump didn't come with one you can buy them separately. Just make sure you ask for a flow check when you buy it.I am the walking Deadman
Hydronics Designer
So my system is just about ready as far the new zones I added. Cross manifold installed. System pressure tested and passed (found several small leaks and fixed them). Purged the system. Just a few small tasks to complete like connecting the return line to the heat exchanger.
I've been searching for this but don't think I've gotten a good answer yet. The old zone in my system was filled with an unknown substance, I assume water, but I don't know if it was mixed with glycol and I am concerned it is full of heavy metals/sediment. The reason for this concern is that I have high levels of iron and maganese in my water, and before moving in there was zero filters or water treatment systems. From the clear pex lines I can see there does appear to be an orange tinge.
Should I flush out the lines in this system? Is there any downside?0
- 87.1K THE MAIN WALL