Nozzle angle & flame impingement
I have a hot water boiler with an old Carlin 101 CRD. The manual for the burner calls for a Hago 60 degree SS nozzle.
The oil company techs have been installing 60 degree All Purpose nozzles for years and the flame has been impinging on the back wall of the refractory firebox and its starting to crack.
I installed a 70 degree SS nozzle and the flame did not impinge on the back wall.
Then I installed a 60 degree SS as per the manual and there is a very slight flame impingement.
My question is should I stick with the 60 degree or go back to the 70?
Thanks.
0 ·
Comments
1.75 GPH is the minimum firing rate on the 101 CRD. Max is 2.75. There are chamber size requirements for each nozzle size, or BTU input. What model boiler? What GPH nozzle is being used?
And hands off!
But, as @HVACNUT says, choosing and installing the proper nozzle is a job for a knowledgeable pro- and you haven't had one work on yours yet.
Where are you located?
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
The nozzle I put in is an actual Hago 1.0 GPH 60 degree. The oil company had been downsizing the nozzle every year from a 1.25 to 1.10 to 1.00 and finally a .85 Delavan All Purpose, someone told me they probably did this instead of cleaning out the heat exchanger and smoke pipe “A down fire Cleaning” he called it.
The boiler was sold by Sears, but when the Abatement company removed the asbestos from the boiler they cut the sheet metal jacket off and any model number that was on the jacket is long gone.
Thru one of the properties I manage I finally found an oil company that actually does a full combustion test, small company with only three techs. They will come sometime in the next month (They are currently tied up with AC work).
In the mean time I set the Air band and Air Shutter as per the manual, I have a Bacharach smoke tester and its reading at #1 on the card right now, but I know that is only one of many measurements to test for and will have the new oil company do a full combustion test. Also being July the boiler is not running on a regular basis so I'm not concerned about sooting it up or doing any damage.
We specialize in Remodeling and maintaining antique homes and I see lots of really old equipment out there that is still in use, every year I see coal to oil conversion, old iron fireman still in the basements, every now and then a house with coal bin still full of coal.
From reading all the posts on The Wall I have learned what needs to be done to maintain oil burners so with this post I'm just looking to increase my knowledge by asking this question.
I will get the combustion chamber measurements later on and post those.
Thanks - Jud
On a Carlin, the air band and shutter are not the only adjustments. Hopefully the techs you have coming will know this.
So where are you seeing all these old boilers? What part of the country?
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
If you didn't set the proper draft first, your smoke test is useless.
Generally with a Carlin, if you have the right head adjustment, and right air band adjustment, with the right nozzle, it will just need fine tuning for perfect true zero smoke combustion.
If you really want to know which nozzle is best you would need to do a full nozzle substitution test.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
My original question in this post was about Flame Impingement on the back wall of a refractory chamber.
Should the flame be fully hitting the back wall and rolling up and above? That’s how it was set by one tech, he told me he always sets it that way…. “No need for combustion testing, I’ve been doing this for years”.
Or should the flame be stopping just shy of the back wall?
Or does it not matter as long as the combustion test numbers are correct?
Its helpful for me to have a basic understanding of things given that we oversee several properties with oil fired units, all told, 6 oil boilers & 1 oil furnace.
Thanks.
Keep in mind the manufacturers chamber dimensions are MINIMUM dimensions in most cases. A slightly larger chamber seldom causes any issues.
It best to work with the MFG dimensions rule of thumb is 100 square inches of floor area for each gallon burned.
so a 1.25 gph burned would be 125 sq inches of floor area=10x 12.5 sq "
As far as impingement or unburned fuel being a concern, again, proper combustion and smoke tests will tell. It's not exactly a yes or no question.
Every year, I seem to work on at least one oil-fired boiler where someone installed a solid-cone nozzle when they should have used a hollow. The resulting elongated flame pattern produces a dark spot on the target wall, and there's usually a lot of soot. I install the hollow-cone nozzle, clean and tune it, and the next year there's hardly any cleaning to do.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
The fact you are running a #1 smoke tells me you are surely off on something. It should be a 0 smoke only.
Rick
He changed the filter but said the oil pump had no strainer and said a Sun Tek would be better but this one was fine for now.
He also upped the pump pressure but did not use a gauge. The paperwork he left said its set at 125.
I have seen pumps with pressure gauges permanently installed. I would like to install a pressure gauge on this pump for future service calls but can’t figure out which port it would go in, anyone care to tell me which port? See photo attached.
Thanks
I would not install a permanant gage on the pump. The oil is under 100psi + pressure. Anyone bumps the gage and it could leak + gages have been known to fail due to vibration and leak. If you put one on I would put a ball valve on the pump first and only open it if your bleeding the pump or checking the pressure, but there is not much room there. It's 1/4" pipe size