Explosion sound Carlin 99FRD, Suntec a2va-7116
Ed. W.
Ed. W. Member Posts: 28
Client hearing explosion sound, intermittent at start up. My guess oil is dripping in fire box after shut down. My diagnoses, put in a oil shut off solenoid. Any Ideas?
  • STEVEusaPA
    edited April 2019
    Probably not it at all.
    Why guess and sell the customer a part (wrong part), when you can go over there and properly test the proper components with the proper skills and tools like a professional?
    Robert O'Brien
    Steamhead Member Posts: 18,501
    First thing I'd look for is delayed ignition. But for the record, IMHO every burner should have at least a delay-on oil valve.
    Consulting
  • STEVEusaPA
    Oh I agree with pre/post purge.
    What if the unit hadn't been cleaned in years, or there's a turd ball on the end of the nozzle, bad pump cut-off, loose wire, bad ignitor...you know, the list goes on and on.
    EBEBRATT-Ed Member Posts: 20,187
    lack of oil flow, plugged filter, nozzle etc
  • Ed. W.
    Filter changed, Nozzle changed, Boiler cleaned.
  • Jellis
    Jellis Member Posts: 232
    draft checked? combustion analysis done? There is a reason for loud start, a oil delay valve is only a band aid, it may make the loud start go away but is not "the problem". did you test the fuel pump? whats the pump pressure and cutout?
    HVACNUT Member Posts: 7,452
    You say "your client", but are you his/her heating contractor? I only ask because you needed 2 sentences for a guess and a diagnosis. A real pro could've done it in one.
  • STEVEusaPA
    I can’t tell if his last post means that’s what he did initially, or that’s what he did and the problem is solved.
    But I do have all I need to know by his first post.
  • HotanCool
    HotanCool Member Posts: 58
    They all can't be Beckett AFGs. Need to learn them all!