Why is my high limit aquastat behaving like a low limit aquastat?
ericmhurtado
Member Posts: 54
Hello, I am having an issue with the high limit aquastat. As you can see from the attached pic, I have disconnected the low limit aquastat wires from the burner because I no longer need it as I have installed a electric heat pump water heater. Why is the high limit aquastat, a honeywell l4006a, clicking and turning on the burner even though there is not a call for heat? Thanks in advance for all of your advice.
It's broke, short in the wiring, or wired wrong.
Probably wired wrong to the oil primary control. In the attached pic, the high limit is connected to the same terminals as the steam thermostat, but according to the honeywell wiring diagram, the terminals should be for a thermostat and a temperature limit control for tankless heater only. So where else can I wire the high limit to? To those two unused terminals above it?0
The high limit is a safety control and should not be wired to the T-T. It should be wired in series to break power to the burner when high limit is reached.
Thanks for the quick response @STEVEusaPA
How can I wire the high limit in series?0 -
I just realized this is steam. Is there a hydronic loop too? If not I don’t understand the need for a high limit.
Pictures from a little farther back would helpThere was an error rendering this rich post.
Yes @STEVEusaPA there is also a hydronic loop. The thermostat for the loop is wired to a Honeywell ra89a relay and so are the circulators. I will send pics soon. Any idea how I can wire the high limit correctly?0
Send pics. I’ll draw up a diagram tomorrow.
I have attached additional pics. One is of the hydro loop with the high limit on the boiler pipe, one circ on the supply and the other red circ on the return. The other pic shows the ra89a relay connections and another one shows how it’s wired.0
Because the high limit is wired to the tt on the oil primary, the r7184p, is the reason why it’s behaving like a low limit. I don’t need the tankless coil, and as a result, the low limit, so I have disabled this aquastat. I would need to rewire the high limit to make it a cold start boiler. Thanks for all the helpful advice with this discussion.0
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 161 Indoor-Air Quality
- 999 Plumbing
- 391 Solar
- 55 Water Quality
- 45 Industry Classes
