Stumped
Steve Minnich
Steve Minnich Member Posts: 2,876
I was in a boiler room today that had a 1.4 MBH steam boiler, piped correctly, short cycling due to inadequate main vents.
Here’s what I don’t get. There was a strap-on aquastat on a vertical return above the water line, wired in series with the pressuretrols.
What is it’s purpose?
Steve Minnich
  • Danny Scully
    Danny Scully Member Posts: 1,465
    What was it set to? Is there a tekmar control or a heat timer control somewhere?
  • Steve Minnich
    It was set to 200F and there was an R & D Contol.
    Steve Minnich
    EBEBRATT-Ed Member Posts: 20,190
    edited February 2019
    What's and R &D control?
    Have seen aquastats on large steam boilers to keep the burner on lo fire until the boiler gets warm. Obviously not used for that.
    Just a guess. Inadequate venting building not heating well radiation short of steam so they shut burner off if the return reaches 200. radiation cold returns hot. Maybe a banging pipe limit LOL. As mentioned could be a "heat established" sensor for a heat timer as mentioned above but not wired that way
    Steve Minnich
  • Steve Minnich
    R and D is a very popular steam control manufactured and used here in Chicago. I see that one more than Heat Timer or Tekmar.
    Steve Minnich
    Mike
  • KC_Jones
    KC_Jones Member Posts: 5,934
    To detect steam at end of main for timing the cycle perhaps?
    2014 Weil Mclain EG-40
    Steve Minnich
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,986
    Steve I have seen aquastats used to keep the burner at low fire until the boiler water reaches a certain temperature.
    Ray Wohlfarth
    Boiler Lessons
    Steve Minnich
  • Steve Minnich
    Thanks guys. I bet that's what it is, Ray. The aquastat for low fire and the operating pressuretrol for high fire?
    Steve Minnich
  • Steve Minnich
    Two stage Weil LGB-12
    Steve Minnich
  • RayWohlfarth
    @Steve Minnich Typically The operating control was set for the desired operating pressure and the aquastat will keep the boiler at low fire until the temperature reaches the setpoint. Once it does, the burner goes to high fire until the call the firing rate or operating control changes it
    Ray Wohlfarth
    Boiler Lessons
    Steve Minnich
  • Steve Minnich
    Thanks Ray. I appreciate the help.
    Steve Minnich
