Radiant 3 zone help
Gta
Member Posts: 151
Hi
I have radiant floor heat throughout my house main living 2000 ft 1500 ft garage, 900 ft bonus room.
The system has 3 zones
1/2 inch pex 11 runs main area
5 runs garage and 3 runs bonus room.
How do I calculate head loss? I’m running bell and gosset Nrf-25 3 speed pumps.
Thanks Sean
Thanks Sean
Oops all runs are aprox 300 ft each0
Longest loop length of each zone.
As @STEVEusaPA said. It’s the head loss of the longest loop. Plus the head losses of the piping to the supply and return manifolds from the pump, and back
Then you need to know the “design flow rate” for the longest loop.
Is this a one pump system with zone valves I assume.?
Flow meters on the manifolds?
Oh I see ok.... it has 3 separate pumps
11 runs main floor .... longest run is 300
5 runs garage longest run is 300
3 runs bonus room longest run 300
Rehau manifolds on all with flow meters
Main set to .5 gpm
Garage set to .6 gpm
Bonus room set to .75 gpm
All 3 separate circ pumps are bell and gossett nrf-25 set in speed 1
Thx s0 -
So if you have flow meters are they reading the correct designed gpm per zone? Or is what you posted what they are reading?
Is this per loop, or per zone?0 -
It’s what they t reading per loop ..... I’ve been having little luck getting proper info .... lol they sold it to me but even the installer I don’t fully think knows all the stuff.
I was told use what works ...🙄🙄🙄...0 -
1/2 pex loops typically run .5- .6 gpm. In theory a load calc and system design would indicate what each zone or loop would require.
Certainly you can adjust them to fine tune loop to your comfort.Bob "hot rod" Rohr
Next question is how is everything heating?
Those are not ridiculous gpm numbers per loop.0 -
The boiler runs a lot .... the rooms are ok the farthest ones are notable as they are a bit cooler ..... are the delta t pumps worth the price? I see taco makes a really cool one .0
In correlation to flow rates above which zones are cooler?0
What is your boiler type?0
Not in my opinionGta said:The boiler runs a lot .... the rooms are ok the farthest ones are notable as they are a bit cooler ..... are the delta t pumps worth the price? I see taco makes a really cool one .
I think you would be happier with a ∆P circulator with a zoned system like that.
Really no value to a constrained ∆ operation IMO.
I have s 23 kw “ lion” boiler
The rooms that are a bit cooler are the opposite side of the house farthest away from the boiler. I’ve tried several times to change the speed of the pumps ... I note the faster circ speeds seem to keep the room more evenly warm.0 -
You're more evenly heating at higher flow rates because you are narrowing the delta of the panel. Especially if the zone is farther away.
Usually shoot for a delta of 10 for floor panels, to keep the panel more evenly heated as you noticed.
You can confirm this by checking supply, and return temps at different circulator speeds.
You could ditch the three circulator zoning set up for one delta p circulator with three zone valves. Saving you money on electricity.
But then you already have the three circs.0