1/8” tap for Gorton #2?
cnjamros
Member Posts: 76
Hi everyone.
Looking to add a Main Vent at the end of the short return in the system pictured here. Hoping to add a single Gorton #2.
The last fitting before the condensate return is a 1-1/4” galvanized elbow. This leg is only 17’ long.
This being my first tap-and-thread, I’m a little apprehensive. I would like to be as cautious and conservative as possible.
By the venting chart, it looks as though I’d be ok with a 1/8” tap for a single Gorton 2, resulting in less drilling by-product (shavings, oil, etc).
Can anyone see any, pardon the pun, holes in my thinking?
Thanks in advance.
C.
Thanks in advance.
C.
If that's all the bigger your hole can be, use a Gorton #D. Its venting port is about the same size. There's nothing wrong with tapping several D vents into the same pipe to get the capacity you want.All Steamed Up, Inc.
Consulting0 -
I can go bigger if needed... The elbow is 1-1/4". But I'm trying to avoid introducing all that debris/oil into the system by drilling a larger hole. The big question: Am I overthinking?
I do have a boiler service set for next week, so perhaps this is the perfect time to do it, since they'll be cleaning the boiler anyway.
The question is, do I NEED to make a bigger hole? A Gorton #2 and a 1/8" open pipe vent at nearly the same rate. Would I be fine tapping 1/8" and using an adapter coupling to install the #2?0 -
I would do 1/4". A 1/8" nipple could be easily plugged IMO.
This might be overkill with the strainers with the blow down caps, that is the reason for the pipe supports. But this had been a 90 year old system that had been badly treated for probably 30 years. A lot of debris/junk inside.
- 167 Indoor-Air Quality