Here is my primary secondary loop with taco sentry valves.
<img src="https://us.v-cdn.net/5021738/uploads/editor/1r/2m98q3c77cqz.jpeg" alt=""
How bad is it?

Comments

  • NYplumber
    NYplumber Member Posts: 503
    Looks good however there should be more straight pipe before and after the Ts before the elbows. This will cause true hydraulic separation. PM me for the formula we use.
    :NYplumber:
  • Snowmelt
    Snowmelt Member Posts: 1,405
    edited September 2018
    I ran out of room. is there anything wrong with doing it in black pipe? in the W/M it also said max between the tees is 12 inch center to center, do you want to come close to that as possible or use a close nipple in between?
  • HVACNUT
    HVACNUT Member Posts: 5,804
    edited September 2018
    The space between the Tee's is fine. What I think @NYplumber is saying is the primary return should be longer before it makes any turns, and the secondary manifold should also have a longer run before any turns.

    Me not being a hydronic Guru by any means, I'd assume the benefits will be restricted but not lost.
    Moving the secondary circuit to a wall would have given you more freedom.

    And black pipe is fine. Makes a nicer looking install IMO.
  • Snowmelt
    Snowmelt Member Posts: 1,405
    hvac nut, I knew he meant longer after the close tee's, I just wanted to be clear on the middle of close tee's in any event it was better then before.
    not to change the subject but I posted this in a face book page and a few guys where telling me that cast iron will rust. I was like no way back in he 50 everything was black pipe.
  • NYplumber
    NYplumber Member Posts: 503
    You will be fine here with the iron. so long as there is no fresh water in the system and no pex that doesnt have an o2 barrier you will be fine. The boiler is a ferrous material just like the black pipe and you dont hear about hydronic boilers leaking every day from normal use.
    :NYplumber:
  • Snowmelt
    Snowmelt Member Posts: 1,405
    that's what I thought