Understanding the L8124E Triple aquastat relay
Options
Joseph_4
Member Posts: 319
Hi I'm trying to get a customer Hot water. His Boiler isnt firing and I see no power is going to B1 and B2
Im used to the L8148E that when u power the control u have 24 volts on t and tv immediatley and when i put jumper on t and tv relay closes boiler fires and circulator comes on..
I assumed the L8124E works same way and when i got there i see power to control and nothing on T and Tv (or 1.8 volts) so i assumed control bad. I swapped out control and getting same result so now I question if Im understanding control correctly.
Any help would be greatly appreciated.
Thank
Joe
HHI Services
Im used to the L8148E that when u power the control u have 24 volts on t and tv immediatley and when i put jumper on t and tv relay closes boiler fires and circulator comes on..
I assumed the L8124E works same way and when i got there i see power to control and nothing on T and Tv (or 1.8 volts) so i assumed control bad. I swapped out control and getting same result so now I question if Im understanding control correctly.
Any help would be greatly appreciated.
Thank
Joe
HHI Services
0
Comments
-
If you have 120 volt power to the control and jump T & TV. 1k relay should pulli in and start the circ pump wired to c1 & c2.
The purner should also start (power on B1 & b2 ) if the high limit and low limit inside the control are calling0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements