EK system 2000 and air handlers

Jon_blaney
Jon_blaney Member Posts: 316
Does a system 2000 play well with air handlers? How does it handle the post burn heat purge to a heat zone air handler? Will the controller keep the fan running after the call for heat is satisfied?

Comments

  • HVACNUT
    HVACNUT Member Posts: 5,804
    What controls the fan now on a heat denand? Thermostat, aquastat, time delay relay?
    The end cycle will also purge heat into the water heater.
    A lot of thermostats allow you to adjust the anticipator if needed.
  • Jim Hankinson
    Jim Hankinson Member Posts: 99
    System 2000 works well with air handlers. Use 4-wire zone valves instead of the 2-wire normally used. The end switch controls the fan. Wire the t-stat to the manager and let it control things, not the air handler.

    Heat is purged to the hot water tank only if that was the last active zone.
  • szwedj
    szwedj Member Posts: 66
    Yes it does when connected properly. You want to wire the air handler thermostat to the system manager on the boiler then use the zone valve end switch to call the air handler. That way the air handler does not get the heat call until the boiler has preheated. Then once the thermostat call is satisfied, the boiler can post purge to the air handler because the end switch holds the call to air handler until the system manager has finished post purging and the zone valve closes.
    Joe Szwed
    Energy Kinetics
    SuperTech
  • Jon_blaney
    Jon_blaney Member Posts: 316
    Will this lead to overheating of the zone because of small water volume?
  • szwedj
    szwedj Member Posts: 66
    Typically there is no problem with overheating, but you can always shorten the maximum post purge time on that zone to 5 minutes.
    Joe Szwed
    Energy Kinetics
  • Jim Hankinson
    Jim Hankinson Member Posts: 99
    Small water volume, fewer BTU's so overheating is not an issue. The complaint if not wired correctly is usually the blower starts before hot water reaches the coil and when the t'stat is satisfied the blower stops while everything is still hot. This results in much lower system efficiency.
  • Jon_blaney
    Jon_blaney Member Posts: 316
    Is the post purge time controlled?
  • HVACNUT
    HVACNUT Member Posts: 5,804
    > @Jon_blaney said:
    > Is the post purge time controlled?

    Yes, using the dip switches, purge time "energy recovery", can be set to a max of 5 minutes, or a max of 20 minutes. Each zone, and the water heater can be set independently.
    EK recently came out with a revised Energy Manager with an LCD display. I haven't been able to play with one yet, but there might be other options with the new control.