Overhead boiler expansion tank
SethYank
Member Posts: 36
I came across this expansion tank yesterday. The circulator is on the return to the boiler, plugged into a wall outlet. The supply and return from the boiler go into this tank and the house supply and return come into the tank also. I am assuming the piping doesn't connect inside the tank. I am trying to figure out how to purge this system, there in no purge in the return from the house.
Possibly a buffer tank?
For an old gravity system?
Only one pump?
Open expansion tank in attic perhaps?0 -
only one circulator that i saw, base board heat, piping is 1 1/4 inch copper running horizontal in basement so don't think old gravity, did not get in attic. I am trying to figure out why the water is going to want to go out to the house and not just short circuit in the tank to the boiler.0
Is this a buffer tank?
Well that's 'different'.
I suspect there must be another pump0
I wonder if there are dip tubes or some sort of diverters/ looks like all the connections down low would just flow across to one another? The air bleeder make me think it is an expansion vessel somehow.
Was it working when you discovered it? full of water? Any other expansion vessel?Bob "hot rod" Rohr
No the circulator was seized, something about running 365 days a year and not being oiled. the tank was half full right at the air vents. I ran into some one who had seen these before and he said they were a buffer / expansion tank. So there must be another circulator some where, but since the customer thinks I overcharged him for expecting overtime on a Saturday afternoon to replace the circulator I wont be going back.2
I dont know that is why I posted it here. some one else has to have seen one of these0
where are you located. Often you find more installations like that in an areaBob "hot rod" Rohr
First experimental attempt at hydraulic separation
