Options
Fizz
Member Posts: 555
WM-SGO3, from 80's, with dirty sight glass half-way. Want to loosen petcock to blow-down, but not sure what to loosen. There's a nut similar to my 2000 SGo-6, on bottom of assembly, but also a detailed-like attachment on nut-do I turn nut, or other attachment?
0
Comments
-
If you want to drain the sight glass regularly, replace the pet clock with a quarter turn ball valve, and some piping to accommodate a bucket to catch the dribbles.
My experience with those petcocks has been: once open-never close!—NBC0 -
Something like this might work? I was surprised to find non-brass friction washers in my sight glass assembly too, since replaced, and this setup with ball valve now in place and working well:
https://www.youtube.com/watch?v=_z8v1YOQcM4 0 -
This 1000 times. I did this after seeing @Steamhead and @Gordo doing it on their installs.nicholas bonham-carter said:If you want to drain the sight glass regularly, replace the pet clock with a quarter turn ball valve, and some piping to accommodate a bucket to catch the dribbles.
My experience with those petcocks has been: once open-never close!—NBC
Makes it super easy to keep it clean.0 -
Here is a quick video of a sight glass blowdown valve in action.
https://www.youtube.com/watch?v=PWaHRD-6bmQ All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
Excellent advice, thanks guys!0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 428 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements