Gas Orifice is 17/64".....off the charts I see...anyone know?
JUGHNE
JUGHNE Member Posts: 11,508
Old NG steamer with 9 X 17/64" drill bit sized orifices. Looks to be .2656, a #1 is .2280.
Does anyone have a chart that goes larger than the #1? At the various WC ratings.
Thanks.
    EBEBRATT-Ed Member Posts: 19,497
    edited October 2017
    Used to have a chart somewhere................Went on Carlins website ez gas burners. They don't have 17/64 but a 9/32 (slightly bigger) is 150,000 and a 1/4" (slightly smaller) is 125,000 so I would think your about 137,500 x9 or 1,237,500 if that makes any sense. that's at 3.5 wc
    Maybe can find something on a burner mfg web site
  • JUGHNE
    This is a 1974 American Standard steamer 1B-J1.
    Nameplate is almost gone. Only the stamped numbers are visible....the printed part isn't quite there.....??G-1010
    Looks like 1,800,000 input/1,440,000 output. Mini input?? 360,000 ?? Could that be right?
    4563 steam Sq Ft. then ?????1252.2
    There is more fire there than needed I am sure. TRV's on most CI rads. Hanging heaters not used etc.
    I just like to check out the numbers etc.
    Thanks Ed
    1,800,000 input x.8 (80% efficiency)=1,440,000 output. That makes sense
    4563 square feet off steam x 240 (btu/sq ft)=1,095,120 btus x 1.33 piping and pick up=1,456,509
    almost makes sense
    Pretty close to the 1,440,000 above
    Looks like they used a pick up factor of1.31492439 LOL!!
  • JUGHNE
    Thanks Ed, I bet that took a lot of scratch paper....who else knows what that is?
    The school is supposed to come up with the original print of the heating system. (1930's) It has upfeed risers, looking for any original air vent locations. Also connected EDR without doing all the leg work of 3 floors.
  • Canucker
    Canucker Member Posts: 723
    So you'll be doing the leg work of collecting the EDR soon? ;)
    You can have it good, fast or cheap. Pick two
  • JUGHNE
    Maint man said they were getting a copy for me.
    Even with it I will still have to visit every room.
    Still wondering about the item on the nameplate......
    "Min? Input? 360,000" ??
    Could it be minimum input 1,360,000?? That would make sense
  • JUGHNE
    There is not a 1 in front of the 360,000. The hammered numbers are very distinct. It does look to say min. in??? above the hammered numbers. Doesn't make sense.
    Thanks.