2 pipe Steam
Jim Robinson_2
Member Posts: 6
Do I leave this kidney shaped air vent? On this 2 pipe steam trapped system I have to replace the boiler and I am thinking it is here for a reason but the guy who installed it is dead!
I've got a feeling this isn't going to end well for the system.
What are your plans for the rest of the piping? What size boiler are you using?
@SteamheadSingle pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
This is something different......vapor/vacuum etc....someone here will probably tell you.
How has it been working with the existing piping (not good BTY) on the boiler?
The old boiler must be leaking?0 -
It's a Dunham 2203 Air Eliminator. I think it looks like a heart, so when I rebuild them I paint them red. Rebuilding one this very afternoon. It stays.
New England SteamWorks
newenglandsteamworks.com3 -
What @New England SteamWorks said.
In this system, the radiators do not have air vents on them. Air exits the radiators through the traps, travels through the dry (overhead) returns and goes out through that vent. Without the vent, the system won't heat well, if it heats at all. There should also be radiator traps piped between the ends of the steam mains and the dry returns. These route the air from the steam mains quickly into the dry returns and out the vent. If these are leaking or stuck shut, the system won't heat well.
And I hope you're not going to re-use the existing steam piping around the boiler. It was wrong from the get-go. What boiler are you going to install?All Steamed Up, Inc.
Consulting1 -
This is a video of Warren Webster's smaller version of the Dunham air eliminator.
https://www.youtube.com/watch?v=YO7_65-uWzw All Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc1 -
Hoffman #79? That's a hot-water vent:JohnNY said:@Gordo, do you think that can be replaced with some creative piping terminating to a Hoffman 79? It seems like the functions are similar.
http://bellgossett.com/steam-specialties/water-vents-model-77-78-79/
You need a vent that can close against steam if, for example, a trap fails open and fills the dry return with steam.
One Gorton #2 is the minimum here. The only vents Hoffman ever made that were big enough for a system like this were the #10 non-vacuum and #11 vacuum vents, and those went out of production sometime around 1930.
Since this is on a "B" dimension rather than an "A" dimension, I would not use a Big Mouth. You need a vent with a float so the vent won't discharge water if the pressure gets too high.All Steamed Up, Inc.
Consulting0 -
Beating once again.
newenglandsteamworks.com2
- 116 Geothermal
- 169 Indoor-Air Quality