How "fast" is Hoffman 40 radiator air vent?
lzr0
Member Posts: 3
Hi,
Is it slow or fast? What approximate number of Hoffman 1A (adjustable) or Gorton sizes it corresponds to?
Thanks.
Thanks.
See this excellent reference by Gerry Gill and Steven Pajek available on the System Help Center of the Main site, and at this link: https://heatinghelp.com/assets/documents/Balancing-Steam-Systems-Using-a-Vent-Capacity-Chart-1.pdf
Appears to be midway between the 2 and 3 setting on a Hoffman 1A , or mid-way between the fixed Gorton 4 and Gorton 5 vent rates.
My experience has been its a nice vent which makes balancing the radiators and room temperatures easy.-1 -
I understood, Gary, thanks.0
Hi again. This chart does not list Verivalve. Do you happen to know how it compares to the slowest vents (like Gorton 4) when it is in Closed position? I am trying to find the slowest one.Gary Smith said:See this excellent reference by Gerry Gill and Steven Pajek available on the System Help Center of the Main site, and at this link: https://heatinghelp.com/assets/documents/Balancing-Steam-Systems-Using-a-Vent-Capacity-Chart-1.pdf
That's true.Gary Smith said:I thump know the Hoffman 1A variable vent at the lowest settings are about the slowest vents, I use them, and they have the advantage that you can increase the vent rate from very very slow to faster if you need to.
I use them too but for the most part in the mid range. I was looking at non adjustable vents.
Here is the venting rate for the Hoffman 1A at each setting and @ 1 Oz., 2 Oz and 3 Oz of pressure
Hoffman 1A Setting 1 0.020 0.026 0.033
Hoffman 1A Setting 2 0.026 0.043 0.056
Hoffman 1A Setting 3 0.100 0.158 0.200
Hoffman 1A Setting 4 0.108 0.160 0.210
Hoffman 1A Setting 5 0.140 0.220 0.290
Hoffman 1A Setting 6 0.145 0.225 0.3000 -
The Hoffman 1a is a good vent but the slop in the adjustment makes it difficult to know whee they are really set at
3PSI gauge0
- 120 Geothermal