How "fast" is Hoffman 40 radiator air vent?

lzr0
lzr0 Member Posts: 3
Hi,
Is it slow or fast? What approximate number of Hoffman 1A (adjustable) or Gorton sizes it corresponds to?
Thanks.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Gsmith
    Gsmith Member Posts: 442
    See this excellent reference by Gerry Gill and Steven Pajek available on the System Help Center of the Main site, and at this link: https://heatinghelp.com/assets/documents/Balancing-Steam-Systems-Using-a-Vent-Capacity-Chart-1.pdf

    Appears to be midway between the 2 and 3 setting on a Hoffman 1A , or mid-way between the fixed Gorton 4 and Gorton 5 vent rates.

    My experience has been its a nice vent which makes balancing the radiators and room temperatures easy.
    lzr0
  • Gsmith
    Gsmith Member Posts: 442
    Revise that last comment, I meant the Hoffman 1A makes the balancing and adjusting of room temps easy, not the #40.
    lzr0
  • lzr0
    lzr0 Member Posts: 3
    I understood, Gary, thanks.
  • lzr0
    lzr0 Member Posts: 3

    See this excellent reference by Gerry Gill and Steven Pajek available on the System Help Center of the Main site, and at this link: https://heatinghelp.com/assets/documents/Balancing-Steam-Systems-Using-a-Vent-Capacity-Chart-1.pdf

    Hi again. This chart does not list Verivalve. Do you happen to know how it compares to the slowest vents (like Gorton 4) when it is in Closed position? I am trying to find the slowest one.

  • Fred
    Fred Member Posts: 8,542
    Most people tend to stay away from the Heat Timer Varivalve. They tend to spit water. The Hoffman #40/41 are about the slowest radiator/convector vent @ .042 CFM for the #40 and .058 CFM for the #41 both at 1 ounce of pressure.
    lzr0
  • Gsmith
    Gsmith Member Posts: 442
    I thump know the Hoffman 1A variable vent at the lowest settings are about the slowest vents, I use them, and they have the advantage that you can increase the vent rate from very very slow to faster if you need to.
    lzr0
  • Fred
    Fred Member Posts: 8,542

    I thump know the Hoffman 1A variable vent at the lowest settings are about the slowest vents, I use them, and they have the advantage that you can increase the vent rate from very very slow to faster if you need to.

    That's true. :) I use them too but for the most part in the mid range. I was looking at non adjustable vents.
    Here is the venting rate for the Hoffman 1A at each setting and @ 1 Oz., 2 Oz and 3 Oz of pressure

    Hoffman 1A Setting 1 0.020 0.026 0.033
    Hoffman 1A Setting 2 0.026 0.043 0.056
    Hoffman 1A Setting 3 0.100 0.158 0.200
    Hoffman 1A Setting 4 0.108 0.160 0.210
    Hoffman 1A Setting 5 0.140 0.220 0.290
    Hoffman 1A Setting 6 0.145 0.225 0.300
  • BobC
    BobC Member Posts: 5,522
    The Hoffman 1a is a good vent but the slop in the adjustment makes it difficult to know whee they are really set at

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge