Power vent timing

SeanR
SeanR Member Posts: 1
For those of you out there that use power venters on oil burner setups, how long is the recommended time for the post purge cycle?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    3 minutes is a good start

    There was an error rendering this rich post.

    billtwocase
  • billtwocase
    billtwocase Member Posts: 2,384
    3-5 minutes. Is the burner's control also post purging? No need to if it is
  • captainco
    captainco Member Posts: 812
    I sold a lot of power venters and a 90% condensing oil furnaces. Like it or not the minimum post-purge we could get by with to eliminate smells and after-drip was 8 minutes. Gas can get by with 3-5 minutes not oil.

    The furnaces I sold came with 5 minutes timers and we had to change everyone to 8-10 minutes.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Wow 8 minutes.

    There was an error rendering this rich post.

  • captainco
    captainco Member Posts: 812
    Much of it had to do with the combustion chamber radianting back into the airtube and heating up the oil in the drawer assembly and creating a delayed afterdrip. This was discovered by a rise in the CO readings more than 30 seconds after the burner shutdown. Sometimes it just had to do with smells and overcoming negative building pressures.
  • billtwocase
    billtwocase Member Posts: 2,384
    Keyword is condensing unit. Non condensing oil unit 3-5 is sufficient
  • captainco
    captainco Member Posts: 812
    Field Controls has an adjustable post-purge timer on their PVO Power Venter for oil and it goes up to 10 minutes, thanks to me. I am sure with a really short flue 3-5 might work but not on longer flues. 8 minutes work every time to prevent the combustion chamber from radiating enough heat back into the airtube and eliminating afterdrip. Without testing for CO for at least a minute after shutdown you wouldn't know if you had this problem or not. That is when trial and error on setting the timing began.