Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Minneapolis-Honeywell
Options
Alan (California Radiant) Forbes
Member Posts: 4,643
mixing valve installed in 1950 and still going strong. Serving copper tubing in the floor downstairs and copper tubing in the ceiling plaster upstairs.






8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
4
Comments
-
love that gauge too! Thanks for the trip down memory lane.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
After digging around the controls a little bit more, I came to find out that the boiler is controlled by a Honeywell aquastat below the eaves on the east side of the house. The original boiler was probably something with a high water content like one made by American Radiator Co., but it has since been replaced with a Munchkin. The Munchkin complains when the aquastat turns on the boiler, but the thermostat hasn't turned on the circulator. I'm tempted to make it a constant circulation system.
This is the oldest outdoor reset system I've ever seen. Those engineers at Honeywell were mighty smart.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
If it's the one I am thinking of they were pretty common. Looked like an aquastat had two bulbs 1 outside air 1 in the boiler. Problem always the capillary length0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements