Power venting duo?
kcopp
Member Posts: 4,663
Customer asked me to look at their "new" homes heating system.
Boiler is a Nat Gas Lennox GWEB8-1E... induced draft.
For some unknown reason they also added a Field swg-4L power venter to the venting...
They both run when calling for heat?
Any idea why?
Any idea why?
This is a chimney vented boiler. In order to direct vent it must be with a power vent. The inducer is only to overcome the resistance of the boiler itself... I have the pdf file for the boiler if you'd like a copy..0
Go figure..... seems pretty odd that that is the case but sure enough, you are correct.0
The whole thing is hooked into an old gravity hot water system.
Its not piped into the system right and short cycles like mad. It just really needs to get through the winter and then it will be replaced w a proper condensing boiler.
ty0 -
Back in 92 when the efficiency standards changed all the furnace manuf made a single furnace that could be either Cat I or III. It was a catastrophe and quickly led to the introduction of Cat I & III specific appliances. All were draft induced. The difference was that while the Cat I appliances were induced the size of the inducer was really only sized to get the air/fuel mixture across the unit itself. From then on, you had to vent it correctly. They were high times, and holy smokes, 25 years ago. Anyway, just because it is induced, it is not "power vented"!1
Right. Induced draft sucks combustion air into the furnace or boiler. It's up to the draft of the flue to vent the combustion products. Some boiler manufacturers allow venting in stainless steel out the side wall on certain boilers, no forced air makers do. Single wall and b-vent leak so without the 2nd ventor fumes will leak into the house.0
- 123 Chimneys & Flues