Ok, so my steam boiler has been working well up until last night. My boiler is only 2-3 years old. It was working yesterday and at some point during the night, it decided to not turn on any more. So, here is what I did in the 15 minutes before i left for work:
Cycled the thermostat - it clicked off, then on again, but boiler didnt fire
Drained enough water out to force the Water Feeder to kick in - nothing happened.
I am thinking it might be something electrical. Its too new that it shouldnt have any internal problems, at least i hope. Anybody else experience this, or have any idea what to test/try next? I am able to work on this, but i need some direction. I attached the IOM of my boiler in case that helps.
Thanks!
Thanks!
Have you had the boiler serviced this year?0
I had it serviced during the summer, tech said everything looked good. It has been working great since i started using it in October.0
What exactly did the tech do as his service?0
it was just a basic inspection to make sure all systems were working correctly.0
It could be the vent damper safety switch, the LWCO, the pressuretrol, or the ignition control. Are there any blinking LEDs on the ignition control?
3PSI gauge0 -
There are no blinking LEDs on the ignition control. I have a vaporstat with a pressuretrol backup that i installed a few months ago that has been working perfectly. How should I go about checking the vent damper safety switch and the LWCO?
Usually when the thermostat kicks on, i hear the vent damper open up, then i hear the ignition kind of buzz 3 times and the boiler fires up. Right now, when the thermostat kicks on, nothing happens at the boiler.0 -
If the vent damper isnt even moving, sounds like the power to the boiler is off. Did you check the breaker? Maybe the transformer blew out. Do you have a multimeter?0
If the feeder kicked on I would assume the boiler has power.
What the crap man? You missed a tiny comment on a public forum while trying to help someone for free? I can't believe you.adambnyc said:whoops. OP comment about "nothing happened" made me think the feeder didnt kick in either
It happens.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Actually, the feeder did not kick on. I feel like there is no power to the boiler, but non of the breakers in my box are tripped.
Yes, i do have a multi meter0 -
If you've got a meter I'd start at the transformer and make sure you've got 120VAC on the primary side and 24-28VAC on the secondary side.IMS47 said:Actually, the feeder did not kick on. I feel like there is no power to the boiler, but non of the breakers in my box are tripped.
You probably already know, but be careful, you're dealing with lethal voltage and current levels on the primary side. If you're not confident in being able to do it safely please don't do it.
That was my plan of action when i get home. I am comfortable dealing with voltage at this level, anything more and i leave it to the pros0
I guess I didnt misread it
. One last basic thing to check. Is the switch to the boiler on? Some homes have two switches controlling power to the boiler, one on the boiler and one near the top of the stairs? Check the switches. 0 -
Yes, i do have two switches, one on the boiler, and one up on a wall behind my washing machine, which is right next to the boiler (dont ask me why). I checked both, and they are both on. There is an odd small box right next to the second switch, that i have not opened. There may be breakers in there that flipped. I will check that as well.0
Could that second switch be a SSU device with a plug fuse under a small lid?
You also might check the blocked flue safety in the draft hood and flame roll out safety above the burners.
Those may require a manual reset........if so that would indicate some other, possibility serious, issue.0 -
Check the damper, there is a switch on it (usually its recessed and easily passed over)... anyway turn the switch to off to bypass the damper and then see if it will start0
Page 14 of the I&O manual show that. Manually opening of the damper for testing purposes.0
You would still need to open the damper by hand, that switch just keeps it from closing on it's own.
Personally I'd meter things out and not play games with the damper until I found out if it's where the voltage stops.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Would the damper or any other safety switch keep the LWCO/Autofill from working?0
No, unless the boiler was miswired. Sounds like it's time for a pro. Where are you located?All Steamed Up, Inc.
Consulting0 -
Did you check that small box next to that second power switch? It should swing open and it probably has a fuse inside.0
Was this a converted boiler and is there a fireomatic and is there a c o detector on the same circuit.....0
Fyi. No power pretty much has nothing to the recent service of the boiler imop0
Ok, so this ended up being an easy fix. I check the two switches, they were good. Opened the small box next to the second switch, and when i did, the boiler kicked on. So i pushed around the wires and the boiler kick off and on. Turns out it was a loose wire. I turned off the breaker, snipped now and stripped the wires, and reconnected it. Everything worked perfect from there on out.
Thanks for all the help guys!1 -
Steamhead, I am located in Easton, PA. I have a house built in 1900 with the original steam system. Its a Tudor style, two pipe system, with a new boiler installed about 2 years ago (before we bought the house). I think i am in need of your expertise to get it running tip top. Send me a message if you can help.0
Bummer on such a day, one before Thanksgiving. Sounds like, from what you are saying, you have no power coming to the boiler. Check electrical connections. If you have nothing on the 120 side, and all your switches are on, check the switches, then check if the breaker didn't go bad. Also, if you are operating off of a sub panel, check it too. You may have had a weird power surge overnight that fried something. I once had 1/2 of my rental unit circuit board go bad and had the HVAC guy figure it out, and not the electrician as AC didn't work and 1/2 of the plugs in the apt. also. I also had a 3 year old pushmatic breaker trip whenever the fridge kicked in... point being, even new breakers can go bad.
As to servicing, after a few years, even if you blow-down the boiler weekly, gunk can build up in the float-type low-water pump switch. Make sure that is openend up and cleaned at the next service.
How's your water level now? If the boiler ran low on water, your low water limit switch may have kicked in. But for this, you'd have something led-like blinking somewhere.
Same goes for the damper. I dealt with this exact thing on one of my hw boilers yesterday. Damper was stuck, and the call for heat was never answered with the flue blocked off. This too would not result in total power loss.
Do post what it was when it's figured out and good luck!
(Haha, I just now saw the resolutuon post! All this happened as I was typing. Glad it was a loose wire at the switch. I'm leaving the rest as others may find it helpful when troubleshooting their own issues.)0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam