Monitor boiler

347
347 Member Posts: 143
Hello all,
Came across this boiler today which I'm told is a Monitor MZ 225c. It is shot cycling (on/off) every minute or so.
The customer needs to reset the boiler every time he wants heat. It looks like he presses a reset button on flue pipe which I think is a limit switch.
I could not find any manual on the job or online for any help.
I attached (I hope) some pictures of the boiler and heater it is connected to. It's a single zone system with the indirect. I think it needs some additional piping but I'm not sure. Any help would be great.
Thanks.





Tor

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • ch4man
    ch4man Member Posts: 297
    wow, i thought i was the only one to ever see one of those.

    French made POS. if it is the flue gas limit thats tripping its scaled up inside and out. I loved how the honeywell ignition control is a single try for ignition. one misfire and its locked out- no heat

    good luck
  • 347
    347 Member Posts: 143
    Thanks for the responce. Do you have any idea where to get a piping diagram or manual? I can access anything on line and have no clue who the local rep is.
  • Dan Foley
    Dan Foley Member Posts: 1,268
    MZ has been out of business for several years. I put in 50+ of these. I still have a few parts. I also have all of the service manuals. Send me you e-mail address.

    @ch4man I second your opinion on the Honeywell module with one try for ignition.
    Rich_49
  • 347
    347 Member Posts: 143
    Dan, I think I sent you a pm, just not sure if it went through.
  • Dan Foley
    Dan Foley Member Posts: 1,268
    @347 Got it. Coming your way.
    Rich_49
  • Here are my notes on where to find parts for Monitor boilers, but they are from 2012 and they may no longer be available.

    6/13/12 Spoke to Rob Kushner (oilman501@aol.com) and ordered parts for Pietkiewicz
    Here is the place
    They are really good.
    Ask for Bob.
    http://www.budnyfuel.com/
    Trenton, NJ

    1/23/12
    monitor parts
    you might want to contact : Nelson & Small on canco rd. in portland, me. / they are, or at least were the northern new england distributor for monitor & toyo stoves..water heaters ..etc.. / may still have parts for your need../ good luck..

    For parts: Northern Heating in Wasilla Alaska has a fair parts selection. 907-376-7515

    Home office: (309)361-9353

    x1 - Sales
    x2 - Tech. support (Nick Russo)
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • 347
    347 Member Posts: 143
    Dan, got it Thank you. ALan thanks for that info. Does any one know what that small rubber hose hanging is or goes to, I could not see it in the parts breakdown Dan sent.
  • Looks like it's attached to the auto air vent.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • kcopp
    kcopp Member Posts: 4,537
    1/23/12
    monitor parts
    you might want to contact : Nelson & Small on canco rd. in portland, me. / they are, or at least were the northern new england distributor for monitor & toyo stoves..water heaters ..etc.. / may still have parts for your need../ good luck..
    .......

    FWIW... Nelson and Small folded up shop and couple years ago.
  • hot_rod
    hot_rod Member Posts: 24,881
    the short cycling could be related to a flow issue. Did you check the onboard pump? What type of distribution piping? Non barrier tube by chance? Could it be sludged up?

    It was't a bad boiler for early condensing day. Certainly more dependable than some of the early Munches.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Also, check that big brass strainer connected to the expansion tank by the braided hose. I've seen those clog up.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab