sizing a distribution manifold
Options
roundrightfarm
Posts: 54
I'm install a boiler with home run distribution, going to 23 radiators, all with TRVs. I'm look at two 13 outlet manifolds. I have the option of 1" or 1 1/4". The price difference is minimal. Design heat loss is 141k BTUH, giving me a flow of 14 GPM at design conditions (delta T = 20), or 7 GPM through each, assuming they are well balanced. So 1" seems more than adequate for my flow, but given that 1 1/4" is basically the same price, are there any other considerations that would make me choose one or the other?
0
Comments
-
I don't know what brand you are considering, sometimes only the connection or ball valve on the end changes, same manifold dimension really. So the 1" should cover your load of 7 gpm.
Branches are usually good for up to 2 gpm, will that cover your largest radiator?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks hot rod. I'm looking at Caleffi. Do know if it is the case with these that only the connection threads are different?
My largest radiators should have a flow around 1GPM0 -
Correct, manifold is identical, just the valves on the end change. The manifolds are unique with a recess for the tubes to lay in, plenty of flow with the square shape.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
thanks hot rod for clearing that up0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements