Split system Ac liquid line sweat in attic
Paul_69
Member Posts: 251
Central Ac ,r22. Air handler in attic and condenser 20ft or so below on ground. No Ac issues. When Ac shuts off and then liquid line then gets cold when off so it sweats in hot attic and makes little water marks. I think this is because refregerant is equalizing after shut down. I guess? I have never seen this in 37 years of Ac servicing. Maybe it has been in places and I have not seen it. Thx
Check the liquid line drier for temperature drop a crossed it. It could be partially clogged. It's also not a bad idea for Any liquid line that runs through an attic should also be insulated to keep good subcooling numbers.0
Refrigerant migration and liquid line solenoid valve.hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
I have had LLSV not completely seating do the cold sweat.
LLFD almost plugged could do the same??0 -
20' of pressure drop when liquid backs out of attic and into condenser could drop the pressure in the liquid line. I could beleive this pressure drop causes the refrigerant to boil, then rapidly cooling below the dew point of surrounding air.
Never seen this with my own eyes, but pretty cool find.
What might make for less of this could be a solenoid valve at the ahu/evap to help keep the migration less and stop the equalizing, or to insulate the liquid line.
But now i'm really curious, what kind of pressure drop is slow enough to let the refer coil-off in the liq line long enough to swet that much?0 -
Paul, where do you live? Thats for temp/humidity #'s. So, can one of you #'s Guys do the figuring on figuring out at what attic temp/RH% will condensation will occur?
Does the lineset rise above the AHU before going out/down to the CU?0 -
Mass. Yes the line is higher0
Another point for all,is this system runs fine.it gets cold when unit shuts off. ll is warm when running and gets cold when shuts off only and in hot attic it sweats and leaves small water stains.0
Silly question about TXVs.
Do all TXVs equalize pressure when the system shuts down? I seem to recall some of them, or all of them, not.
Second question, wouldn't insulating the liquid line solve the issue assuming the system is working properly?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Yes it will Chris,just like to learn.I have suggested insulating to customer as a fix,just like to know why something is different.
Thx0 -
With this being R-22, it must have been in service for some time.
If the line dripped previously it would have been noticed.
Something changed.....does the LLFD get cold after shut down?
Harvey's compressor valve test is a good idea, easy to do (not in attic anyway).
Is this a fixed orifice or txv?0 -
Most TXVs are non bleed so they don't equalize. We just did a job with long line across attic. Tech rep said mfr. calls for armaflex on the liquid line across the attic so we did. Probably a piston meter and cold refrigerant is leaving the evap into the liquid line. Should loop the lines up above the coil then down as a trap.0
- 15.8K Strictly Steam