Unexpected perc to running system in vacuum on 3cph
Fizz
Fizz Member Posts: 555
Noticed cellar is toasty-warm since changing t-stat setting to 3cph.
  • Fred
    Fred Member Posts: 8,542
    If it's not a finished space and used accordingly, I'm not sure that is a Perk. Are the steam pipes insulated well?
  • Fizz
    Fairly well except for boiler risers and header.
  • Fred
    I would insulate the risers and header as well. Make sure the boiler isn't running so frequently and for such short periods, at 3CPH, that it is primarily keeping the mains hot for minimal added comfort in the living portions of the house. Of course comfort is a matter of personal preference but I would try 2CPH and see how that works for you.
  • Fizz
    Good advice, however only have 3 settings and 2 cph is not one.
  • PMJ
    PMJ Member Posts: 1,275
    As far as comfort is concerned cold floors are generally not desirable. And hot mains mostly just warm the floor above. Drafty cold areas below are pretty much just a bad idea if you care about comfort in the first floor. Insulated mains and returns are a must and when properly done just don't lose much.
    I keep my mains hot with 3cph and I think it evens things out a lot. With 2 pipe (which I think Fizz has) and natural vacuum there is basically no preheat time at all and steam from the mains continues to flow to the rads with the burner off. I have found only benefits to more cycles and see no negatives.
    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
  • Fizz
    Yes I do have 2 pipe(Richardson System) in vacuum. It hasn't been extremely cold this winter, but pipes stay hot, and on re-firing heat gets to rads in few minutes-several minutes quicker than no vacuum, also, 3cph has provided steady heat comparable to what hot water heat provides.
  • vaporvac
    vaporvac Member Posts: 1,520
    edited March 2016
    I second @Fred , and suggest you insulate them soon. I did mine recently and it has completely changed how quickly my system heats and how well it distirbutes its steam. Major difference that I wasn't expecting since my mains have their original asbestos insulation intact.
    My tstat only gives me 1 or 3as a hydronic choice.... no 2 CPH. :( I think running it 3 is probably just as efficient as 1 or even two IF one has vacuum. I hish I had two CPH as a choice because my rads stay warm for a really long time in vacuum and three might be too much. However, I suspect with 3 CPH you can probably stay sub-atmopheric on re-fire?
  • SWEI
    SWEI Member Posts: 7,348
    I don't understand why at least one of the major thermostat makers hasn't opened up the options there. Why not give us options for 1, 1.5, 2, and 3 CPH? Doing so would be trivial from a firmware prospective.
  • ChrisJ
    ChrisJ Member Posts: 17,042
    VP8000 does.
    Well, 1,2,3 etc
  • SWEI
    edited March 2016
    I've seen several posts here where 1 CPH was to little and 2 CPH was too much. 1.5 CPH seemed like a good idea for those systems.
  • Fred
    The 7000 Series has 1,2,3 and 5. I don't know if the incremental differences between each setting is smaller or not I.E. is a "2" setting closer to "1.5" ? From what I have read, at least with the Honeywell's the CPH is actually a programmed temp anticipation rather than a fixed number of cycles per hour. I think they said @ 1CPH the thermostat will allow a full 1 degree swing before the thermostat call for heat. at 2CPH is is like 3/4 of a degree and at 3 and 5 it is incrementally less for each of those settings.
  • vaporvac
    edited March 2016
    Yes, the HW6 series only has 1 and 3,4,5,6 as choices. All of my prior programmables DID have 2 as an option. I'll have to check what Brands they were as I kept them as back-ups. I called HW and they said 2 CPH couldn't be added. I bought the least expensive programmable wi-fi and it was also on sale as they were changing the cover plate. I guess I got what I paid for, but the $$ difference was substantial. I put that money into NBPiping insulation.
    When speaking to HW's tech support, they said their algorithm is based on multiple sensors for temp AND humidity and something else. They didn't mention lesser degree swings on other CPH settings, but that makes sense, @frank . Edit: @Fred :) MY house wouldn't lose that much heat in 20 or 30 minutes, otherwise.
  • ChrisJ
    Who's Frank? :)
  • vaporvac
    edited March 2016
    LOL! That's why I need the edit function. Maybe he'll pipe in when he get notification.
  • MarkS
    MarkS Member Posts: 75
    Incidentally, newer Honeywell thermostats like the WiFi 9000 do not have an option for 2 CPH. Your options are Steam (1 cph) or Hot Water (3 cph). And according to HW tech support, there's no "super user" back door menu option to plug in a 2.
    1890 near-vapor one pipe steam system | Operating pressure: 0.25 oz | 607 sf EDR
    Midco LNB-250 Modulating Gas Burner | EcoSteam ES-50 modulating controls | 70 to 300 MBH |
    3009 sf | 3 floors | 14 radiators | Utica SFE boiler | 4 mains, 135 ft | Gorton & B&J Big Mouth vents
    vaporvac
  • Fizz
    Then insulate header and risers I shall. Thanks to all.
