Sensor Accuracy
Thanx.
My Lochinvar sensor does the same thing.0
How do you adjust the curve for a 5* higher/lower outdoor temperature?bmwpowere36m3 said:just set the curve and adjust as needed.
It would be helpful if the boiler board allowed input of a outdoor temperature difference or the actual outdoor temperature. If the sensors are going to be inaccurate, it seems it would be better if they erred on the minus side rather than the plus side.
Honestly I wouldn't worry about it. If it bothers you that much, then simply adjust your HI and LOW ODT points on the curve 5* over.
This is assuming a ODR curve with 4 points: LO ODT, HI ODT, LO ODT water supply temp and HI ODT water supply temp.0 -
It would be a nice option to be able to calibrate a sensor on board. Some thermostats have this ability..
Does the sensor meet the specified ohm readings outlined in the manual?0 -
The Alpines have the calibration that applies to wired and wireless sensors. Ohm it from boiler on wires and than ohm the sensor. May be interference. Don't parallel line voltage wires, florescent lights etc. Or you can use shielded wires.0
woodshed said:
The outdoor sensor for the boiler is not accurate; using an old style mercury thermometer, the temperature reading from my truck and the temperature reading from the HO's car all show the same outdoor temperature reading. The outdoor sensor reading is 5* higher. The boiler manufacturer sent me a replacement sensor but it's 5* higher as well. So, isn't an accurate outdoor temperature sensor the key part of ODR? BTW- the outdoor sensor is a 12k not a 10k sensor. Any ideas on this or how to correct it?
Thanx.
How long is the wire run to the sensor and what gauge wire? Sometimes there is a restriction in the installation regarding the wiring.Bob "hot rod" Rohr
I'd be interested in a solution to this issue as well as I have discovered my outdoor reset is inaccurate. And unlike indirect DHW tank sensors, you can't really replace or calibrate outdoor reset sensors with 3rd party tools; and that's a shame.0
sound like all you need to do is "fit the coefficients of a third order polynominal in the log-resistenance values to best match the inverse temperature values"
http://www.mstarlabs.com/sensors/thermistor-calibration.html
Kurt would know, I think it can be corrected with the correct resistor. On our solar demo trainers we us 10K POTS and little rebel resistors to adjust the value wherever we need to "trip" the control functions.Bob "hot rod" Rohr
That sounds like a very looong weekend Hot Rod
Gordy -the sensor chart shows the reading is supposed to be 36,130 for 32* and I'm reading 37,000; however the outdoor temp is actually 27*Gordy said:It would be a nice option to be able to calibrate a sensor on board. Some thermostats have this ability..
I tried another 12k sensor and the spread is even larger.0 -
When you look under the hood to see what makes it tick..It's amazing how they can build them so small and accurate.
I imagine there is an acceptable tolerance from the builder of that thermistor?
It needs to work across a wide temperature range. For solar that temperature can be well below 0° in Alaska to over 500°F on a stagnant evac tube solar collector header.
We test them with ice water, and boiling water to see how they match the resistance chart.Bob "hot rod" Rohr
Either the thermistor is out of spec, or the ADC in the boiler controls is. As long as the error is even moderately consistent, I would probably just adjust the ODR points until things get comfortable.0
Wouldn't I adjust the HI and LOW ODT 5* lower?bmwpowere36m3 said:Honestly I wouldn't worry about it. If it bothers you that much, then simply adjust your HI and LOW ODT points on the curve 5* over.
It's reading 5 too high, right? No, move both points 5 degrees higher.0
I think woodshed is correct.
My sensor reads high and the math was saying I would need 145 degree water but mine was at 140 and was fine during the below zero cold spell.0 -
Although you guys are talking about raising the outdoor temp instead of water temp so BMW may be correct.0
If it's actually 5* colder out than the sensor reads, you should raise your setting so you get higher SWT to compensate for the colder actual...like BMW states.0
- 87.2K THE MAIN WALL
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 75 Pipe Deterioration
- 6.4K Radiant Heating
- 15.6K Strictly Steam