EDR for this Convector and its bigger brothers.
The Steam Whisperer
Member Posts: 1,313
I have a house with a bunch of these on the first floor....the second floor is US Radiators standing iron. I think they are from around 1930 and in Chicago. I couldn't find them in EDR. Any ideas?
The Steam Whispererer
Check on page 257; U. S. Copper Convectors, Type RC.
Presuming they are 48¼" long:
4" deep - 25.3 EDR
6" deep - 36.4 EDR
8" deep - 48.5 EDR
10" deep - 50.5 EDR8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Might also be American Radiator Co "New Murray Radiators", which were actually convectors. Pages 133-135.All Steamed Up, Inc.
Towson, MD, USA
Oil & Gas Burner Service
Consulting0 -
Those are the New Murray Radiators like Frank mentioned0
Another bit of info......These are cast iron, not copper or aluminum. So they wouldn't be either of those two.To learn more about this professional, click here to visit their ad in Find A Contractor.0
You might have to settle for something close. Check on page 250 which shows Capital Cast Iron Convectors made by U.S. Radiator Co. Choose convector dimensions closest to yours and that should get you in the ballpark.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Yes, that's were I was headed.
Thanks everyone!To learn more about this professional, click here to visit their ad in Find A Contractor.0