EDR for this Convector and its bigger brothers.
I have a house with a bunch of these on the first floor....the second floor is US Radiators standing iron. I think they are from around 1930 and in Chicago. I couldn't find them in EDR. Any ideas?
The Steam Whispererer
  • Check on page 257; U. S. Copper Convectors, Type RC.
    Presuming they are 48¼" long:
    4" deep - 25.3 EDR
    6" deep - 36.4 EDR
    8" deep - 48.5 EDR
    10" deep - 50.5 EDR
    Steamhead Member Posts: 18,208
    Might also be American Radiator Co "New Murray Radiators", which were actually convectors. Pages 133-135.
    All Steamed Up, Inc.
    Towson, MD, USA
    Oil & Gas Burner Service
    Consulting
  • EzzyT
    EzzyT Member Posts: 1,377
    Those are the New Murray Radiators like Frank mentioned
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,313
    Another bit of info......These are cast iron, not copper or aluminum. So they wouldn't be either of those two.
  • You might have to settle for something close. Check on page 250 which shows Capital Cast Iron Convectors made by U.S. Radiator Co. Choose convector dimensions closest to yours and that should get you in the ballpark.
    Yes, that's were I was headed.
    Thanks everyone!