Can you....

Options
Paul S_3
Paul S_3 Member Posts: 1,261
Provide " FULL OUTDOOR RESET " to a system with a 80% cast iron atmospheric boiler....with the tekmar 256 ( customer purchased control and asking me to install ) by eliminating the boiler minimum temp option. ...I know the ci boiler cannot see less than 140f because of flue gas condensation. ...can I use p/s piping with A boiler protection valve?....this system has a indirect water heater. ...when the heater calls I would be using relays to take the reset control offline to have boiler fire up to 180f....or should I tell customer to scrap the 256 and I purchase the 356 and use injection pumping. ...with the 356 I know I can achieve this without the boiler protection valve...since the 356 has boiler protection option.....thanks in advance Paul S
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Options
    Yeah just put on a mixing valve to protect the boiler, or an aqua smart...:)
    The boiler protection option algorithm (in my opinion) is wrong for this application and creates short cycling.
    Another option is same as above with a buffer tank. Let the boiler only run to charge the buffer tank (like an indirect).

    There was an error rendering this rich post.

  • JohnNY
    JohnNY Member Posts: 3,230
    Options
    I've done it many times. It's far from ideal, but some people want "the most efficient system" they can get, until they see the price. Then you gotta put something together for them. This is one of those things.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • ChrisJ
    ChrisJ Member Posts: 15,700
    Options
    JohnNY said:

    I've done it many times. It's far from ideal, but some people want "the most efficient system" they can get, until they see the price. Then you gotta put something together for them. This is one of those things.

    It's a shame most don't realize the most efficient system is a well insulated and sealed building eh? :p
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    True but we're building and renovating so tightly fresh air needs to be introduced to help with air quality
    E-Travis Mechanical LLC