Boiler cycling easy fix
My system is a six zone system with zone valves and a ModCon boiler. I access the run time and cycles. The boiler was cycling 40x an hour during the winter months. I have a Taco ZVC control.
I disconnected the end switch from the control going to the boiler so the zones will not call the boiler. I took the largest zone hooked it up to a separate ZVC controll with that end switch calling the boiler and boiler pump and the system pump. I adjusted the outside temp curve to a lower at point temp so it would run longer to satisfy the house temperature.
The boiler only calls for the main zone. The other zones will call and wait till the main zone call for heat.
The boiler only cycles 4-6 times an hour. My therms for last year dropped by 20%.
The final test is that my wife hasn't complained about the heat.
SWEIkcopp
  • unclejohn
    unclejohn Posts: 1,833
    Then be sure not to tell her about the fix. When she finds out she's not as warm as she thought she was your in trouble.
    CanuckerSWEIRich_49