Boiler Corrosion Protection
Josh_S
Member Posts: 17
in Gas Heating
I'm still in the process of making my fhw system more efficient. This was a gravity converted system, there's a 3" main and 2" main that run off the 1 1/4" copper from the boiler. Now with a system that large it takes AGES for the water to heat up. It'll run for about two hours getting up to 170° from cold start. It has a system bypass (not ideal but I'm not changing it at this point) that is throttled to 1/3 of the way open. I have a Grundfos 20-42 circ pump set on III. Now with a system that large if I throttle down the bypass a tad bit can I turn the circ to the II setting without compromising too much on the flow through the system?
With the current setup on a cold start it takes 15 minutes to reach Crowns specified point of 120°. Is that acceptable? I'd like to try to get it down to between 5-10.
You really want constant circ for a gravity system. Is the system direct pumped, or primary-secondary?
The 120°F number is a bit for returning water on a conventional boiler. If that's the supply temp, you are going to have issues.0 -
Here are some pictures. Basic setup, no primary/secondary.0
Assuming the boiler is in good shape and burning cleanly, I would install a Taco iSeries-R mixing valve and set up the system for constant circulation.0
At some point funds will allow for that, I'm pretty handy but copper pipe is not something I deal with. In the meantime what can I do to maximize system heat while allowing enough to cycle back to the boiler? Also have these pictures of the heat exchanger granted they aren't very good but it seems to be in pretty good condition. Boiler was installed in 08'.0
Like, will turning back the circulator speed reduce system flow by a huge amount?0
Look at an ESBE thermic valve. You're going to have to spend some money, that is probably your cheapest option. While you're at it, replace that scoop, that's useless plumbed that way, with something like a spirovent.0
The diagrams I have seen show a single circ, with the alternate position on the return ( not ideal). I believe I was looking at Danfoss?0
- 110 Chimneys & Flues
- 981 Plumbing
- 387 Solar