No thermal roll out fuse
Options
Fred Rappuhn
Member Posts: 107
I am installing the conversion kit from a cycle pilot system to a gold control system on my Weil Mclain HE2 boiler. Every thing is going very well until I see that this boiler never had a thermal roll out fuse installed above the burners. I see where it's supposed to be installed but looks as if it hasn't been there for many years. My original manual shows that it supposed to be there!! I have ordered one and will install, but how much of a problem was this in past operations?????
0
Comments
-
would guess it wasnt an issue since the boiler didnt burn up. Someone got very lucky...0
-
I wouldn't say they got very lucky, I'd just say they weren't unlucky. I don't believe they even became a thing until somewhat recently.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
-
I figure the guy who pulled it got lucky. Removing a safety of any sort is a nightmare waiting to happen...whether they "became a thing" or not.0
-
If someone had removed it, they're just not too intelligent.lchmb said:I figure the guy who pulled it got lucky. Removing a safety of any sort is a nightmare waiting to happen...whether they "became a thing" or not.
I've considered adding a second to mine. They're cheap and they can save your life.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
-
Honestly there are so many unsafe boilers, out here, someone needs to step up and address it.....Didn't the do gooders get the ins. Companies to require updating your oil line..not sure cause I never had anything to do with oil ,except removing the dirty old crap
0 -
Not sure what to say to this post other than, wow.j a said:Honestly there are so many unsafe boilers, out here, someone needs to step up and address it.....Didn't the do gooders get the ins. Companies to require updating your oil line..not sure cause I never had anything to do with oil ,except removing the dirty old crap
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
Wow means ?ChrisJ said:
Not sure what to say to this post other than, wow.j a said:Honestly there are so many unsafe boilers, out here, someone needs to step up and address it.....Didn't the do gooders get the ins. Companies to require updating your oil line..not sure cause I never had anything to do with oil ,except removing the dirty old crap
0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 418 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements