comments welcome
lchmb
Member Posts: 2,997
newest steam project. Day one went well til the threader died..Thoughts or suggestions are always welcome..
If you ask JStar,nicely, maybe he would thread you a nice big header. I'd lose that horizontal union in the header. I believe check valves are required for that thermostatic mixing valve, and I'd be more comfortable with back-flow prevention.Maybe over-kill, but......0
Is that 3" pipe?
I personally prefer to have a bit more separation between last riser and first main takeoff.0 -
Thanks... sadly it's not 3" pipe. Dont have the equipment to do it. I just realized the spacing was wrong between the last riser and first take off.. Burnham wants at least a 5" nipple..can fix that tomorrow...as far as the mixing valve, it has built in check valves...I've never bothered with back flow since it has the checks and I assume (bad word) that would take care of that...0
What model boiler is that?0
Megasteam 5130
Make sure you have some pitch on that header and on the mains as well. If it were me, I'd also change out those vents and put some Gorton #2's on those returns.0
Pre-cut nipples! That's how we do it.............lchmb said:Thanks... sadly it's not 3" pipe. Dont have the equipment to do it.
Consulting0 -
Thanks for posting pics.So do you guys think this system as is piped will work well.@jstar how much more in labor and cost will a 4 inch header cost to this system.Thanks .Honestly its a nicer install than you would come across on most cases and obviously 3-4 inch will operate well but with 2 risers and drop header low pressure how much of a difference will it make,I am asking out of curiousity as I have done similar installs and was quite pleased.1
wow brutal crowd around here....Just kidding.... as much as I would like to go with a larger header, I work for a fuel supplier. I pushed like a banshi to get them to go with the premade header's for the install's I've done. Hard to sell bigger when Burnham makes a pipe kit and it come's in 2". As far as the pitch, hard to see but there's plenty on it and the main vents will be changed in a few weeks when i go back to skim it again. I like to let the boiler treatment work for a bit first...0
Did you get that pipe kit from Burnham? I was going to assume you did because of the wye you have that seems like it can't be found anywhere.
I agree with others on a larger header, but I also understand the position you're in.
It's pitched good towards the equalizer you say? That's good to hear.
I also like the cardboard on top of the boiler. It's nice to see someone protecting it like that while laying things on it.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
I am game for that.Lets get some guesses on the outcome and maybe start a pool proceeds go to your choice.Would be nice to know.
It would be interesting to know the true difference between the two. Now if someone can explain (I come here to learn) how that two feet of pipe on the drop header will save even 5% of fuel I would appreciate it.0
well..cant say i've made this perfect but think it's improved greatly over what I started with. Thanks for the lesson's though...:) always want to learn to do it better...0
- 62 Biomass