Updating baseboard heating system

Options
Mothra
Mothra Member Posts: 24
Bought a home, built in 1895, currently in the middle of a remodel. The propane boiler quit this past winter, so I am looking to purchase new. The old boiler was exhausted into an old existing chimney, but i want to break that dependency, so i was thinking a high efficiency model that i can vent out the side of the house. Since the boiler quit, some of the existing baseboard burst, so i'm looking to replace that, as well, running PAP as supply/return lines. I'm looking for advice on brands to investigate for the boiler and baseboards. I was thinking about frostapex for feeding the baseboards, but unsure about what all 'accesories' i need. Could someone assist me on that, as well?

On a side-note, I'm also installing radiant floor heat via warmboard, so i'm not sure exactly how to heat the baseboards and the radiant floor, if i can do it through one system, or if i should put the warmboard through the hot water heater. Any expect advice would be very much appreciated.

Comments

  • Mothra
    Mothra Member Posts: 24
    Options
    Also, would i be better suited using 3/4" Frostapex rather than the 1/2"? i was leaning towards the 3/4". thank you, again
  • Steamhead
    Steamhead Member Posts: 16,833
    Options
    Where are you located?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Mothra
    Mothra Member Posts: 24
    Options
    Northwest Ohio. I did a hand calc of my heat loss, and i think i had came up w/ 113k btu/hr. It's a two story, old farmhouse, with a third story attic that isn't heated at the moment. I am planning on eventually installing an outdoor wood boiler, gassifer in an outbuilding, but that is probably a couple years away. Admittedly, thinking about all the infrastructure i'm planning on updating leaves me a little overwhelmed. The hot water sourcing also needs to be updated.
  • Mothra
    Mothra Member Posts: 24
    Options
    Should i be looking at radiant panels instead of baseboards?
  • hot_rod
    hot_rod Member Posts: 22,131
    Options
    I prefer then look and disability of panel rads, easy to zone with TRVs. They may pair better with the Warmboard.

    Best to have a load and design done, this will tell you about which emitters may or may not fit.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mothra
    Mothra Member Posts: 24
    Options
    hot rod said:

    I prefer then look and disability of panel rads, easy to zone with TRVs. They may pair better with the Warmboard.

    Best to have a load and design done, this will tell you about which emitters may or may not fit.

    So I should do a room by room heat loss calc and see how each system 'fits'?
  • hot_rod
    hot_rod Member Posts: 22,131
    Options
    yes, you need the info for each room to properly size the heat emitter.

    Ideally you would like to design the heat emitters to cover the load on design day with 130F or less supply temperatures.

    So it is important to select the heat emitters to match the low supply temperature to leverage the efficiency of the boiler.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mothra
    Mothra Member Posts: 24
    Options
    Ok, thank you. Tonight i will take measurements and try to come up w/ proper calcs for each room. Thank you, again.
  • Rich_49
    Rich_49 Member Posts: 2,766
    Options
    Research Ohio programs or spend the money to have a blower door performed to determine Air changes per hour . This one element is the single most important thing to get ti right .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • hot_rod
    hot_rod Member Posts: 22,131
    Options
    It may be tough to get an accurate infiltration number on a leaky old farmhouse. We came across leaky old homes home that we couldn't even get pressurized with a single blower door wide open!

    Ideally you would want that number after all the structure upgrades are done. It sounds like that is an ongoing project?

    As such the load number you get now, with the home in the "leaky" phase, will be much different than the number after the tighten-up.

    Wood gasification boilers generally have a buffer tank with them as the don't come in a lot of size choices, 40, 60, and 80 K outputs are common. Also, you want to run them hot, and for long cycles, at least a full firebox worth of run time, for best efficiency. Run them full out, store the excess energy in the tank.

    Bottom line.. the boiler you calculate now may be oversized after the home is upgraded. With a modulating type boiler you have some "wiggle' room for de-rating them.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mothra
    Mothra Member Posts: 24
    Options
    Rich said:

    Research Ohio programs or spend the money to have a blower door performed to determine Air changes per hour . This one element is the single most important thing to get ti right .

    Do i need to complete this calculation for the basement and attic?

  • Mothra
    Mothra Member Posts: 24
    Options
    hot rod said:

    It may be tough to get an accurate infiltration number on a leaky old farmhouse. We came across leaky old homes home that we couldn't even get pressurized with a single blower door wide open!

    Ideally you would want that number after all the structure upgrades are done. It sounds like that is an ongoing project?

    As such the load number you get now, with the home in the "leaky" phase, will be much different than the number after the tighten-up.

    Wood gasification boilers generally have a buffer tank with them as the don't come in a lot of size choices, 40, 60, and 80 K outputs are common. Also, you want to run them hot, and for long cycles, at least a full firebox worth of run time, for best efficiency. Run them full out, store the excess energy in the tank.

    Bottom line.. the boiler you calculate now may be oversized after the home is upgraded. With a modulating type boiler you have some "wiggle' room for de-rating them.

    You are very much correct in saying that is an ongoing 'upgrade'. Right now, i am working on the second floor of the home. All the second story exteriors walls will be spray foam insulated and backed w/ R-19 batting. The plan would be to carry out that method of 'tightening' the remaining house up throughout the process.

    I'm trying not to close stuff up now and then have to go back and have to tear holes in the wall/floor once i have my heating situation figured out. I thought i was set on going back to BB heating, well, b/c that was what had existed in the home previously. I am all about the mindset of doing things right the first time, however, and want to make sure i am making the best decisions for the infrastructure moving forward. That led me back to here and looking into panel radiators. I'm pretty sure I could make home runs with all the rads that are needed, if that's the direction i want to go. I'm planning on doing the pex work and attaching the rads, but i don't think i'm skilled enough to install/design what is needed from the boiler, expansion tank, manifold system, etc. To say i'm trying to get my arms around everything is an understatement. Thanks for your continued advice/help.
  • Rich_49
    Rich_49 Member Posts: 2,766
    Options
    Although it may be difficult to get the house to -50 Pa , the attempt should still be made . A quality home performance contractor should be quite able to identify glaring trash and temp address those areas to get the house depressurized enough to identify the smaller stuff . Let's face it , Mothra is performing these upgrades anyway . Someone versed in identifying the problems and making adequate recommendations should be done anyway .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • Mothra
    Mothra Member Posts: 24
    Options
    Here is what i got for my heat loss calcs:

    Downstairs + Upstairs total

    TL Heat loss @ 60F = 73462
    TL Heat loss @ 70F = 86683
    TL Heat loss @ 80F = 98439
    TL Heat loss @ 90F = 110132
    TL Heat loss @ 100F = 121943

    that was using http://www.usboiler.net/heat-loss-calculator.html

    I did not include the third story attic or the basement
  • Mothra
    Mothra Member Posts: 24
    Options
    I have the heat loss breakdowns for each individual room, as well
  • hot_rod
    hot_rod Member Posts: 22,131
    Options
    lower than the original 113K estimate. Common sizes for mod-cons 80, 100, 110, 120. If you chose a 100 or 110, it would modulate down as then load lessens after upgrades get completed.

    There are a lot of features and functions available on boilers these days to help dial them in. I like the Lochinvar Knight as one top brand. The ramp delay function and other features would allow you to easily and efficiently de-rate the output as the home takes it's journey to completion.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mothra
    Mothra Member Posts: 24
    Options
    What is the typical heat loss design temperature?
  • Mothra
    Mothra Member Posts: 24
    Options
    Anyone have any suggestions for panel rads and the accompanying pex needed to complete the heating circuit?