what should i charge to when replacing the TXV
Mcro1986
Member Posts: 8
long story short lennox unit bad txv wouldn't adjust 30 degree superheat found brass shavings inside the txv.
I ended up flushing the lines changing the filter dryer and txv. i used an Emerson txv instead of another lennox txv. now my question is, do i charge the system to the condenser requirement of a 6 degree approach and 3 subcool or what Emerson wants a 10 degree subcool?
In my experience 10 degrees of sub cooling will rarely get you in trouble no matter whose unit you are working on.good luck0
I'd go with the equipment manufacture recommendations. But as Zep said 10* sub cool shouldn't hurt.0
Mcro, There aren't too many places in a system to get brass shavings, possibly they were copper?
Yea , KindaSorta, 10*SC will cover your butt for every AC for every brand . So going by the CYA rule then you will be OK. So, if your system "needs" only 2*SC , CYA and get 10*SC, or if your system "needs" 8*SC then 10*SC will still CYA. Its a "catch all" rule, for "typical" installs, that fall within the "piping height vs length" chart of each Mfrg . Don't a few CU say on their nametags 6*SC is their "target SC", 6*SC sure limits the piping "H vs L" thing.
Q here, the ACTUAL REQUIRED SC of a 50' horizontal lineset is the same REQUIRED SC as a 50' lineset that goes up vertical 35'. NO WAY ,NO WAY, NO WAY.
My BIGGEST concern was/is the fact that lots and lots of Techs don't know the REAL story of SC , or worse they DON'T CARE. If all they do is typical residential/light comm then they CYA and do the "Target SC thing" and they are "good to go", I agree mostly/ some times. I come from a more Commercial/Industrial background (Carrier, Governaire) and "knowing" how to FIGURE OUT SC was/is normal. Now, all of these #'s and charts and guidelines are ALL FOR ONE REASON ONLY, and that is to ensure that the TXV/metering device has a "FULL LL " feeding the TXV, under all "normal" operating conditions. Having a full SGMI at the CU does not guarantee a full SG at the TXV. I've put SGMI at the TXV and CU on some systems "just to see" or I use my "electronic SG tool" to "see" whats happening at the TXV.
There are still Techs that say that just USING a SGMI WILL cause the system to be overcharged. HOGWASH. Overcharging a system is due to an "un-knowledgeable" Tech, plain and simple1 -
WOW all the abbreviations......... Yea, I'm lost. Print it in Aerobic. At least I can go on line a decipher it...:-) Hey Terry Only kidding. What is a CU?, You are talking 1 adem 12....0
Evacuate, weigh in the appropriate charge. Adjust for pipe length and airflow to achieve proper indoor delta T. Lennox has the charts and info. Weigh in gets it right every time.0
Lennox does like a lower subcool than some. We put in an Allied heat pump the other day, under the conditions, called for 1° subcool! Personally I think do what the condenser manufacturer calls for, they know the system.0
John am I reading you right? 1 *Sub/cool? Min 8* 10-14 w/ tx more like it. If that were the case, ( not knowing what you are actually looking at) Just pipe the discharge line into 4 linear foot of coil and there you go. I respectfully would like to know your source of that information because it is and makes no sense.
Peace'
Mike T.
I have never seen a 1* S/C.......
Peace;
Mike T
That was correct, they wanted 1° subcool under the conditions we had at the time. We were surprised. It's a chart right on the door of the unit. 2 ton 14 SEER heat pump.0
I see a range of 8-10 subcool on the Trane 410a stuff, nomenclature states plus or minus 3. Finding 12 is the sweet spot, with low 50s discharge temps. Recently got the SMAN3, we have a tempestuous relationship, as I'm acclaimating to the precision of it, learning to trust it!0
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements
