Twinning Kit
Options
RJMCTAFO
Member Posts: 113
I am in the process of bidding a new hvac system for a liquor store. I am in the early stages but it looks like the problem of having the need for more AC than heat capacity is gonna be a problem. I am having a heat loss/gain done by the wholesaler to verify the numbers given to me by the owner.
Heating load is only 115k
Cooling is gonna be 7.5 tons
I have done twinning on gas many years ago. This customer wants to stay with oil. Is there anyone that has used a kit with an oil setup? Who would make one? All my research only shows gas kits. I want to be able to stage two 65k units for efficiency.
This kit looks like it would work fine on an oil fired unit.
http://www.alpinehomeair.com/related/io-656.pdf
Anyone have any experience to share in this area?
Thanks
Heating load is only 115k
Cooling is gonna be 7.5 tons
I have done twinning on gas many years ago. This customer wants to stay with oil. Is there anyone that has used a kit with an oil setup? Who would make one? All my research only shows gas kits. I want to be able to stage two 65k units for efficiency.
This kit looks like it would work fine on an oil fired unit.
http://www.alpinehomeair.com/related/io-656.pdf
Anyone have any experience to share in this area?
Thanks
0
Comments
-
This is the only non- oem one I have used. They make a good product.
http://www.jacksonsystems.com/products/jackson-systems-universal-twinningparalleling-kit.html0 -
Do you know if this control will alternate the lead unit? Or will I need to install something to take care of that.
I did come across that but was not sure of product quality. Good to hear a word of mouth endorsement.
Thanks for the help!0 -
I don't know of any hot air specific control that does that. You have to do the the old school manual switchover.0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 62 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements