Weil Mclain GV-3 locking out on low temp

Options
burto
burto Member Posts: 7
hi guys, have a GV-3 Series 4 Gold gas boiler feeding two hydro-air units. Unit is intermittently shutting down on low return temp. If temp drops below 140 degrees the bypass circ tries to mix some supply to raise temp. Would like to loose this feature any thoughts

Comments

  • icesailor
    icesailor Member Posts: 7,265
    Options
    That feature is there for a reason. Disable it and destroy the boiler with cold water returning. The condensation destroys the cast iron HX.
  • burto
    burto Member Posts: 7
    Options
    yeah your right. I ordered a new return water sensor, maybe that will help. last week it was below zero so that didn't help.
  • burto
    burto Member Posts: 7
    Options
    installed a new return water sensor. installed a low limit on supply and set to 150*. Being a cold start boiler , this should help ,when both of those hydro units kick on they suck the heat right out of boiler.
  • icesailor
    icesailor Member Posts: 7,265
    edited January 2015
    Options
    burto said:

    installed a new return water sensor. installed a low limit on supply and set to 150*. Being a cold start boiler , this should help ,when both of those hydro units kick on they suck the heat right out of boiler.

    You need to read the I/O manual for the correct settings. When properly set, you will not "suck all the heat right out of the boiler". The system pump is supposed to stop. The boiler pump is supposed to keep running.

    If it is doing what you describe, you have turned it into a "cold Start Boiler" and you will be defeating the purpose of the boiler design.

    Is it piped as the I/O manual describes?

    Here's the I/O manual for a GV Series 3 boiler.

    The control strategy is supposed to limit water going back into the boiler to 130 degrees. If it is getting lower, it will kill the boiler.

    http://www.weil-mclain.com/en/multimedia-library/pdf/weil-mclain-pdf/products/discontinued/discontinued-boilers/gv-boiler/gv3manual.pdf

  • burto
    burto Member Posts: 7
    Options
    thanks for more of your input and the manuals. I will re-think the whole thing and ask if the call came back in. Ill take some pics if I go back. I could see the amps on the motors changing(modulating) between supply and bypass but there so quite.