EDR of this Radiator
cdm
cdm Member Posts: 77
IM looking for the EDR of this radiator. I,ve looked in Dans E.D.R. 'Every Darn Radiator', without any luck. The radiator pictured is on a one pipe steam system. 20" high X 5" deep with 14 - 2" wide sections, for a O.A. length of 28". Any help is really appreciated.
cdm
  • j a_2
    j a_2 Member Posts: 1,804
    31.5 EDR….U S Boiler calls it a radiant radiator…Some call it a sunrad….In the recessed install such as yours you can subtract 10 percent from 31.5 that would be total EDR for a one pipe steam system
  • j a_2
    The subtraction is for output not for total EDR load…I was not sure why you asked for it so I just thought I would clarify that….Sorry If I confused matters..
  • JStar
    JStar Member Posts: 2,752
    You can use the ratings for SunRad radiators. 2.25 ft2 per section.
  • cdm
    Hatterasguy ; Radiator is cast iron (not a convector). ja: Thanks for EDR data - looking for EDR on a stand alone unit - good to know derating of (10%) as a wall unit. star: Thanks for the SunRad input - that fits well with what a contractor told me from his experience. cdm
    shyheim
  • ChicagoCooperator
    ChicagoCooperator Member Posts: 363
    edited January 2015
    Isn't that essentially this?
    http://www.governaleindustries.com/govray.cfm
    As I understand it, it provides both convection and radiant heat.