Honeywell mercury steam valves
Brutus
Member Posts: 2
I am looking for help troubleshooting valves that are staying open
Staying open
Is your system 2-pipe, or 1-pipe?
I suspect a 2-pipe system, with some Honeywell traps which will not close when the steam arrives.
Any trap from that period has been designed for low pressure, such as below 1 psi, so is your system operating in that range?
Check the pressure, and make sure it is below 16 ounces. A good gauge will be needed , from gaugestore.com.
Replacement capsules are available for traps from tunstall inc.--NBC0 -
Take some pictures
of these units and post them here. Let's have a look at them.All Steamed Up, Inc.
Consulting0 -
That's a Zone Valve
the mercury switch probably functions as an "end switch" which can do things like start the burner when the valve opens.
You may be able to get a new head unit for this thing. If not, you'll have to replace the entire unit. We've had good luck with Belimo zone valves on steam- these are ball valves rather than globe valves and don't restrict the steam flow as much.All Steamed Up, Inc.
Consulting0
- 50 Industry Classes