Midco Radiant burner....results of first heating season

The Steam Whisperer (Formerly Boilerpro)
Member Posts: 834
My Burner Tech, Brad, installed a Modulating Midco LNB1000 on an old Pacific Steel boiler. While the combustion numbers on high fire were almost the same as the existing modern conventional burner, the fuel usage was dramatically different. Brad ran the numbers, correcting for degree days, and found over a 30% drop in fuel usage with the new burner. I suspect about 1/2 this drop is due to the modulation, but the other half is probably due to the better heat transfer of the radiant design. The installation was on a larger single zone, single pipe steam system.....no TRV's.
Looks like I'm going to start selling a lot of these
Looks like I'm going to start selling a lot of these
The Steam Whisperer (Formerly Boilerpro)
Chicago's Steam Heating Expert
Noisy Radiators are a Cry for Help
Chicago's Steam Heating Expert
Noisy Radiators are a Cry for Help
0
Comments
-
Not bad
for just changing the burner. What was in there before?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Wow, that was quick....
I think it was a Power FlameThe Steam Whisperer (Formerly Boilerpro)
Chicago's Steam Heating Expert
Noisy Radiators are a Cry for Help0 -
Modulating control
How was that Midco controlled?
It does look like the way of the future.--NBC0 -
Control system
I would still like to know how to control these burners.--NBC0 -
homemade modulating burner
http://news.discovery.com/tech/videos/visualizing-dubstep-with-a-rubens-tube-video-140613.htm0
Categories
- All Categories
- 84.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 44 Chimneys & Flues
- 1.8K Domestic Hot Water
- 4.8K Gas Heating
- 120 Geothermal
- 156 Indoor-Air Quality
- 3.1K Oil Heating
- 57 Pipe Deterioration
- 799 Plumbing
- 5.5K Radiant Heating
- 371 Solar
- 14.1K Strictly Steam
- 3.1K Thermostats and Controls
- 54 Water Quality
- 39 Industry Classes
- 80 Job Opportunities
- 22 Recall Announcements