Options
dandutcher87
Posts: 3
in Gas Heating
i have never seen anything like this before we have 3 furnaces about 100,000 btu non condensing induced draft all going off on high limit that is on draft motor outlet. I took flu pipe off and there is a strong draft from chimney i do not have proper tools to check but it appeared ok. I am getting 4.7 02 and about 160ppm co sometimes fluctuating a bit +-20 ppm. flu temp is about 400F. There appears to be plenty of make up air. all 3 furnaces are doing the same thing.
other notes:
filters clean
ambient room temp 70
gas pressure 3.5" manifold side
natural gas
3 furnaces in same room common venting
other notes:
filters clean
ambient room temp 70
gas pressure 3.5" manifold side
natural gas
3 furnaces in same room common venting
0
Comments
-
Is this a home
Or a business? Sounds like you have a sever negative pressure in the space.0 -
air flow
How about your temp rise? Is it right according to the nameplate?0