Thinking of replacing existing pump for a Taco Bumble bee pump
Total1
Member Posts: 44
Thinking of replacing existing pump for a Taco Bumble bee pump .
<a href="https://www.taco-hvac.com/en/products/products.html?current_category=405">https://www.taco-hvac.com/en/products/products.html?current_category=405</a>
On my Vitodens 100 system .
Ideas ?
Ideas ?
Why?
Why?0 -
Looks like a...
WIlo you have installed. Very good pump, pretty much all I use. I second the question...Why? do you have any problems with system?0 -
Like the idea of the pump
Like the idea of the pump adjusting to the boiler temperature and keeping the delta T the same . No problems at all with the system , but the new pump would use 85 % less power and has a cool look factor ..0 -
and noisy
The bumble bee is much louder than normal pumps. If thats a factor.Tom
Montpelier Vt0 -
WOW
LWCO is in the wrong place though it doesn't matter because the boiler won't fire anyway if you don't make the flow switch..With the boiler needing a min flow rate of 1.7gpm across the HX and you are not piped pri/sec wouldn't recommend it unless your going to run it in a constant pressure mode.
What's with that zone valve and the ball valve? Some sort of by-pass?There was an error rendering this rich post.
hmm
Why is the LWCO in the wrong place ? It is the highest in the loop , where would you put it ? . The zone valve / bypass is for the room / tunnel under the garage to get enough flow to start the boiler .0 -
huh?
That's why the boiler should have been properly piped primary secondary. Sure hope you never need more then 6.2gpm...LWCO is useless so it doesn't matter...There was an error rendering this rich post.
Dont mess
Dont mess with a high head hx and dt. If you slow the flow too much you will loose more then you gain.:NYplumber:0 -
ok
With this on demand boiler , since it keeps no water warm when it shuts off , and the pump is controlled by the boiler also , I have no need to circulate the water when it is off . The Gas inspector wanted a LWCO installed , I even quizzed him on why one is needed with the flow switch . This boiler is ONLY heating my garage , room / tunnel below the garage , and later project floor heat for the bathroom in the basement , all is good and thanks for your input . I will keep it how it is . To keep around 1100 sq ft of floor heated it averaged out to be 1 $ per day @ 60 F , even when it was -36 C .0