what to do
drhvac
Member Posts: 190
in Gas Heating
allot of times when checking drafts on furnaces, I find the draft pressure to be higher than it should be. I know ideally we are looking for about a ,-04" draft on a conventional induced draft 80% furnace, but what would you do if the draft was higher? What if the draft was anywhere from - .05 - .15? If you check the sizing of the flue is right, if the gas pressure is right, how do you correct this? Could you put a barometric damper in the flue and adjust it with that? I'm just curious to see what you guys would do if this was your job? Obviously the furnace would work more efficiently if you could slow the combustion gases down where they should be so that more heat is extracted from them. What would you do?
Draft
You got it. Install a draft control damper with a safety spill switch. You should also block off the integral draft hood or remove the external draft hood.0 -
damper
So a weighted barometric damper would work? Do you do this on your equipment ? I don't know what you mean by this " block off the integral draft hood or remove the external draft hood " Could you explain please? On n induced draft system there is no draft hood, unless your talking about an older furnace with no inducer motor.0
- 116 Geothermal
- 15.8K Strictly Steam