is copper nipple ok to connect lwco to steam boiler
boiled
Member Posts: 7
I have two-pipe steam heat with a Weil-McLain model E-7 series 2 boiler and had to recently replace the McDonnell Miller Series 67 LWCO. The new (identical) LWCO was connected to the boiler upper & lower tapping with what appears to be copper nipples. is that ok? From reading the posts here, I thought only black pipe was acceptable, at minimum, copper only acceptable for wet returns.
Some additional details in case makes a difference: I believe this copper piping came as part of the "quick hook-up fittings" with the Series 67. This LWCO is also connected by its upper tee to a pressure guage, pressuretrol, and a vacuum breaker (Hoffman 60).
Copper nipple?
Its probably brass, and should be ok.0 -
looks like copper to me?
I have attached two photos. "before" is the piping on the original LWCO and this looks like brass to me. "after" is the piping on the new LWCO and the pipe connected to the boiler looks like copper to me. is this worth asking the heating contractor to fix?0 -
Red brass...
You're fine.
In my 36 years, I've never seen a "copper" threaded nipple. You can make them using male adapters and copper pipe, but I've never seen a one piece solid copper nipple. Too expensive.
ME0 -
threading
Thank you for reassurance, that makes sense about (red) brass and the threading.0 -
Real Copper Nips:
I've seen some very old true, solid copper nipples on old water piping. Like on old showers. Never larger than 3/4".
I had a couple of 1/2" nipples with brass caps that I used over and over for test purposes where a nipple was going to be run through the wall. I changed them to black after the test and inspection so that some nefarious sheet rocking installer didn't borrow them, never to be returned to me.0