low water cutoff
tmc
Member Posts: 12
Anybody having problems with McDonnell miller pse 802 probe type low water cut offs? installed 4 burnham independence steam pin 4 and pin 3 boilers and all are shutting off on low water when there's plenty of water in glass. I removed probes which all looked clean but wiped them off anyway, reinstalled and still had same problem. Boiler will fire for about 1 min low water red lite will flash boiler will shut down, water level rises from condensate, boiler fires and then repeats cycle. Once again, this happens with water level above probe.
Through a glass emptily
Could the initial cutting oil+ return rust have clogged the gauge-cocks, so the glass is not showing the true level? A new install has a lot of junk floating around in the system.
Could the probe be electrically insulated with Teflon tape?--NBC0 -
Ditto
Ditto NBC. Make sure the probe is grounded (no tape on threads). Been there, done that.0 -
low water cutoff
doubtful guage cocks are clogged, this happened right from initial start up, but i'll check it out. As far as Teflon on probe as I mentioned on last post they were cleaned.I have a feeling there may have been a bad batch of low water cut offs. any other ideas?0 -
Dirty power?
Those probes are so electronic. Could there be a power problem: bad grounds, etc?--NBC0 -
LWCO
Make sure the factory jumper is screwed down tight. Check the other wiring connections as well. I've had a loose jumper from the factory before. It would run for a minute, then rattle loose and shut down.0 -
problem solved
replaced low water cutoffs with new ones, all 4 boilers working perfectly.0 -
Good to hear
Did the counterman say anything about a defective batch?
3PSI gauge0
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 163 Indoor-Air Quality
- 71 Pipe Deterioration
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
