gpm

Paul S_3
Paul S_3 Member Posts: 1,261
Hey everyone.... This question is regarding a snow melt system with a mixture of 30% glycol....from the manifold through the 5/8" pex loops (6 of them) the GPM for all 6 of them is 6.84 GPM(1.14GPM per loop)....The head loss for the MANIFOLD is 4.5 ft HD....my question is how do I figure the size of the pipe from boiler to manifold (snow melt load=81,225 btuh/h) do I use 1"?....and how do I find the head loss from boiler to manifold, and do I add it to the 4.5 ft hd from the loops?....need this to size pump...thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • Gordy
    Gordy Member Posts: 9,546
    Supply return piping

    Should be sized to carry the BTUs, and flow rate required for the load. Yes the supply/return piping is additive to the manifolds head loss.



    You might squeak it out of 1" with a bigger circ, which brings higher head losses, or go to an 1 1/4, and get buy with a smaller circ.
  • Paul S_3
    Paul S_3 Member Posts: 1,261
    gordy

    Thanks for response....so if I use 1" 1/4"pipe because using 1" would be at it's max with 82000 BTUs.....how would I find the head loss of the 1" 1/4"pipe it's about twenty feet both ways and about 6 elbows?...thanks Paul S
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Gordy
    Gordy Member Posts: 9,546
    Calculations

    http://www.copper.org/publications/pub_list/pdf/copper_tube_handbook.pdf



    http://mobile.engineeringtoolbox.com/



    To invaluable links.



    In the copper .org hand book you will find head loss for various pipe sizes fittings , and types of copper pipe. Enjoy
  • Rich_49
    Rich_49 Member Posts: 2,766
    Can you say

    Snow melt using a Bumble Bee Circ . 42 watts to melt snow ? If you can keep the head pressure in the S&R section below 4 ft you can use the Bumble Bee for this system and keep the Delta T wherever you want it .