chilled water coil delta t
zepfan
Member Posts: 457
does anyone know if there is a formula to find what the air temperature drop should be across a chilled water coil, if the gpm,airflow,and water temperature drop is know? thanks to all
Temp. drop
Delta-T = (BTUH / CFM) / 1.08
Approximately.
http://www.refrigtech.com/Knowledge_Center/Knowledge_Troubleshooting_AC_System.pdf
Check out page 11 for a chart based on indoor wet bulb.0 -
You Should
Get 10* F drop.0