Can a Taco Bumblebee
ced48
ced48 Member Posts: 469
be set to maintain a minimum pump speed? I see nothing in the manual that addresses this.
  • Rich_49
    Rich_49 Member Posts: 2,781
    Bumble Bee
    will maintain a set point , Delta T, or constant power (set speed) . It will operate at which one of 4 speeds you want it to in CP mode . Just program it to your conditions .
    732-751-1560
    Rich McGrath 732-581-3833
  • ced48
    I Got That, But
    how about Delta-T, but with a set minimum operating percentage, like other Taco variable speed pumps?
  • CMadatMe
    CMadatMe Member Posts: 3,086
    Pump Is Going
    Operate on its curve just like any other pump when put in a fixed speed mode. You cannot fix the pump speed. Why would you want a fixed speed?
  • ced48
    The Reason Is-
    I am piping direct, no prim/sec, a modcon and I would like to be able to use the variable speed feature to maintain Delta-T, but I also must be sure of always having a certain minimum flow thru the boiler. so I thought I could set the pump to always maintain a certain percentage output, and let it do what it wanted, as long as it maintained the preset minimum.
  • SWEI
    SWEI Member Posts: 7,348
    Boiler minimum flow rate
    Is specified at high fire.  If you run the pump ∆T it will track the boiler output so you don't actually have to worry about minimum flow.  If the boiler goes off on limit, you will know you got something wrong -- might have to dial back the ∆T 5F or so, but not any kind of a safety risk.
  • Rich_49
    edited July 2013
    Ced48
    What boiler are you proposing this piping arrangement for ?  What type of emitters will you be using also ?
    732-751-1560
  • CMadatMe
    edited July 2013
    Yuppers
    Kurt the other thing direct pipers forget is as they increase system head they reduce the gpm flow across the boiler, thus increasing the needed delta-t to get full output.. Minimum on a PT110 is 5.5gpm to get the full output at high fire. That would mean you were running your system on a 35 Degree Delta-T. How many guys do ya think understand that?
  • Rich_49
    Not Enough
    of em Chris !  Why would you increase a header that must be 1 1/4 to  1 1/2 " ?  That would cost 100.00 , we can't do that !  I think it's part of the design as you solder syndrome.
    732-751-1560
  • ced48
    A lochinvar WH 55
    limited to 70% on the heating side, 75 feet of Slant Fin baseboard. Split loop system, with about 6 feet of head, 2- 90 foot sections. Heat loss around 30,000, or less-
  • Rich_49
    WH55
    does give the installer the option of using a var. spd.  pump for the boiler .  At 20 Delta literature says  3 GPM .27' , Yeah the bumble bee will do that @ 9 watts .  Make sure about your direct piping , they do recommend Pri / Sec in the Notices ( pg 37) .  Have you thought of the CDN040 (cadet boiler) ?  Smaller BTU , closer to your 30K required .
    732-751-1560
  • SWEI
    CDN040
    Also a lower minimum firing rate (9k versus 11k) and about 30% less cost.
  • ced48
    I Don't Like the-
    HX on the Cadet-bought the Lochinvar for a couple of hundred dollars more-beter computer too- As far as prim/sec, Locvinvar is okay with it-does not void warrantee. I can't see spending $400+ on a circulator when a $175 will the same thing, more or less. Thanks for the suggestions, though.
  • ced48
    I Mean Lochinvar-
    is okay with directing piping on a small system like this, as long as I provide the required minimum boiler flow-
  • CMadatMe
    edited July 2013
    Required Minimum Flow
    Is what is needed when you need the full btu/hr output of the boiler. If you don't need it then its not required. As long as you maintain the flow needed at the minimum modulation rate then your ok.. You'll be at the minimum end of the modulation rate much more then you will ever need the max end of the modulation rate.
    When direct piped the only thing that can change the pump flow is the pressure drop or ft of head in the system. I believe you said 6' of head. So pick up a pump that will move the required flow based from your heat loss. If the boiler is 55,000 and the loss is only 30,000 why would you ever need the full out/put of the boiler?
    On over sized pump is just going to reduce your system/boiler delta-t which could lead to boiler short cycling.
  • ced48
    Yes, About 6 Feet
    of head-So, I will be just fine letting the Bumblebee maintain a 20 degree Delta-T? Sounds like the boiler will shut down if minimum flow is not being achieved, requiring a differential adjustment to the Delta-T. I also just realized that the pump will give me a wattage usage readout, so I'll know how much of the pump's capacity is being used. Taco warns that the GPM readout is less than accurate, so I can't go by it. Using never more than 70% of the boiler;s capacity, required flow should be minimal. I'll bet I'll be running at 35% or so most of the time. Prim/sec just seems silly in my case-
  • CMadatMe
    Minimum OutPut of the Boiler Is What?
    There's your minimum flow..
  • ced48
    Minimum Output -
    about 9, minimum input is 11- So are you saying if the flow drops, the boiler will modulate down to be inline with that flow rate? I am trying to learn all I can, not just install a system that works and not know how or why it works. I appreciate your help, Chris, and all the rest of you who have made suggestions.
  • CMadatMe
    Boiler Doesn't Modulate on Flow
    Modulates base on delta-t....flow carries btu/hr based on that delta-t..
    Inutput is 11,000 btu/hr - You'd need to move 1.1gpm at low fire on a 20 degree delta-t. Flow kills you when you cannot move the btu/hr being created in the HX/Boiler out of it. You could then flash to steam.
    This isn't anything new. It's done everyday across the pond with boiler pumps controlled by the boilers control logic to match pump flow to the modulation rate.