Boiler cleaning? Blaa! Who needs it?!
STEAM DOCTOR
Member Posts: 2,509
Pictures worth a thousand words. Converted gravity system with no bypass to return. Low return temps. Flue pipe crumbled in my hands.
Airtight systems
who needs them? While you're at it, go ahead and run that cast iron boiler with 100F return temps -- it's tough enough.0 -
Only if
The boiler is oversized enough SWEI.0 -
Sarcastic
I hope everyone understands that I was being sarcastic. The old(leaking) boiler was piped
without a bypass, thus insuring very low flue temps (this is a converted gravity system). I am sure that this was a contributing factor to the immense sooting and the poor condition of the flue pipe. Anyway, that boiler has been disassembled and will be removed tomorrow. The new, properly sized and properly piped boiler will be going in within the next few days(I hope). New boiler will have bypass from supply to return,pumping away etc.0 -
cleaning
Ironic thing is that there was a boiler brush sitting on top of the boiler. The brush looked pretty clean0 -
Fitting
This is a picture of a single fitting that is used for supply and return to the radiator.0 -
Sarcastic
I hope everyone understands that we were, too.0 -
Yes
Sarcasm ,
And a boiler bypass is not 100% insurance against low return temps to the boiler.0 -
Boiler bypass?
A boiler bypass will allow much of the return water to bypass the boiler and go back to the supply therefor bypassing the boiler. Reducing the flow in the boiler mill allow cooler water to enter the boiler and reduce condensation.
Many try to do this with a system bypass that takes hot supply to cold return which is the opposite of what should be done on residential boilers. When boilers had larger water volume a system bypass was a good thing.
Today with much less water volume in the cast iron boilers we need to reduce the flow into the boiler to get the water temperature up quicker. To quote the late great Gil Carlson " thermal stress and condensation is a result of extremely cold water entering the boiler or coo water at a high flow rate." While we cannot control the temperature with a system bypass we certainly can control he flow rate with a boiler bypass. Adjust the flow to a 20f - 40f delta-t in the boiler and things will work fairly well. Hydronic s Institute states that a boiler bypass sytm will usually give ou 3 times the low in the system than through the boiler. Been using the boiler bypass for years with no boiler issues.0 -
Thermostatic bypass valve
Is usually the best option. ESBE, Caleffi, and LK all have options.0 -
Thermostatic bypass
+ 1. 100% protection.
Should add there are a lot of variables that will allow a boiler bypass to work properly, and some that will not. Usually with a mix of emitter types its best to use the thermostatic bypass valve.
Say you have some baseboard, and rads in a deep setback zone, and boiler is calling on another zone. If the boiler is close to high limit, and deep setback zone calls its a good recipe for boiler shock/condensation. Especially if the boiler is sized properly, and the deep setback zone is large volume.0 -
Brainless bypass
works best when the boiler is significantly oversized. If you size correctly, and actually want to get all the available BTUs out of the boiler, you either need a thermostatic valve or a suitably oversized pump.0